Hi all,

New to the forum! Quick background on me: I have a degree in electrical engineering and spent many years working with qualified electricians on house re-wires. I never qualified as an electrician as I went down the IT route but I can rewire a house with no concerns - not that I would as I'm not qualified!!

A friend of mine asked me to review the electrics on his new extension as he is not happy with the work. Here is what I found:

1. None of the back boxes are earthed. Not a failure but poor practice

2. Loose socket back box and broken light box (missing lug).

3. Ring main cable passing through back of lighting back box ( switch box is level with socket in kitchen).

4. Breakers labelled wrong on the new DB.

5. Live wire sticking out the wall with no termination block! I fixed this one as super dangerous.

6. Live wires sticking out the ceiling with no termination block. Also dangerous but out of reach. Not fixed.

7. Armoured cable missing gland and outer casing not earthed.

8. Light switch in bedroom not screwed in to back box. I fixed this one as dangerous.

Photos attached of some of these. The builder did the electrics and signed it all off. There are a number of issues with the extension- not just the electrics. If I was an inspector I would not have passed it! However, poor practice does not necessarily equate to a Part P failure. So my question is do any of the above actually constitute as a failure?

Thanks in advance,
Glenn
 

Attachments

  • [ElectriciansForums.net] Is this a Part P failure?
    IMG-20221226-WA0000.jpg
    552.7 KB · Views: 127
  • [ElectriciansForums.net] Is this a Part P failure?
    IMG-20221226-WA0001.jpg
    213.6 KB · Views: 109
  • [ElectriciansForums.net] Is this a Part P failure?
    IMG-20221226-WA0002.jpg
    196.4 KB · Views: 126
Following the "sign off" by the builder, has,
an Electrical Installation Certificate been issued by the builder,
and also a Building Regulations Compliance Certificate received back from the Local Authority after notification by the builder?
 
Hi all,

New to the forum! Quick background on me: I have a degree in electrical engineering and spent many years working with qualified electricians on house re-wires. I never qualified as an electrician as I went down the IT route but I can rewire a house with no concerns - not that I would as I'm not qualified!!

A friend of mine asked me to review the electrics on his new extension as he is not happy with the work. Here is what I found:

1. None of the back boxes are earthed. Not a failure but poor practice

2. Loose socket back box and broken light box (missing lug).

3. Ring main cable passing through back of lighting back box ( switch box is level with socket in kitchen).

4. Breakers labelled wrong on the new DB.

5. Live wire sticking out the wall with no termination block! I fixed this one as super dangerous.

6. Live wires sticking out the ceiling with no termination block. Also dangerous but out of reach. Not fixed.

7. Armoured cable missing gland and outer casing not earthed.

8. Light switch in bedroom not screwed in to back box. I fixed this one as dangerous.

Photos attached of some of these. The builder did the electrics and signed it all off. There are a number of issues with the extension- not just the electrics. If I was an inspector I would not have passed it! However, poor practice does not necessarily equate to a Part P failure. So my question is do any of the above actually constitute as a failure?

Thanks in advance,
Glenn
Sounds like your answering you’re own question. I’d be referring more to BS7671. Is this ‘builder’ a member of a scheme? How was the work notified? Leaving exposed live conductors!
 
Just a point, back boxes do not need to be earthed if they have a fixed lug. This is not bad practice in any way.
It's not good practice, either.

Not all light switches have an earthing ring.

I would rather fit a fly lead as there is always the chance of the back box becoming live.
 
Absolutley nothing wrong with it. Please point me to a regulation that states otherwise.
I didn't say it was a requirement, and I didn't say it was bad practice.
But as said, it's not good practice.
Best practice is to fit a fly lead.
Try reading GN8
 
The builder is an approved NIC EIC contractor and he has issued the certificate. I just don't understand how he can issue it with live wires sticking out the wall!

And yes the armoured cable connects to the main 100A incomer.

I'm very tempted to report him.
 
The builder is an approved NIC EIC contractor and he has issued the certificate. I just don't understand how he can issue it with live wires sticking out the wall!

And yes the armoured cable connects to the main 100A incomer.

I'm very tempted to report him.
Waste of time

Just give them a price to do the job properly
 
If the builder/sparks has issued an installation certificate that implies all is compliant with BS7671 and within timescale for building regs, there is no reason why a Part P certificate wont be issued (Did it come straight from the builder/sparks?).
A building inspector wont re-inspect the works done.
Your only recourse is to report it to NICEIC but I dont hold out much hope of them getting involved unless perhaps you can stress how dangerous the live wire situation was.
 
Your only recourse is to report it to NICEIC but I dont hold out much hope of them getting involved unless perhaps you can stress how dangerous the live wire situation was.
Take more than that. Odd unterminated live wire is fairly standard on new builds these days. Was on the one my son bought, last year.
 
Take more than that. Odd unterminated live wire is fairly standard on new builds these days. Was on the one my son bought, last year.
Probably tend to agree but how many get reported to NICEIC? I think mostly would get reported to the site agent.
Hopefully the NICEIC would act on one or two of them
 
The builder is an approved NIC EIC contractor and he has issued the certificate. I just don't understand how he can issue it with live wires sticking out the wall!

And yes the armoured cable connects to the main 100A incomer.

I'm very tempted to report him.
Why not contact the contractor and raise the concerns you have with him first.

The Niceic will say the same thing.
 
It's not good practice, either.

Not all light switches have an earthing ring.

I would rather fit a fly lead as there is always the chance of the back box becoming live.

I'd also add that chances of a back box becoming live in NI are significantly lower than in GB as there are few circumstances where cable sheath will be in contact with entry point of box. Cables buried in walls are enclosed in conduit and those in stud walls generally enter boxes through a PVC female adaptor that won't easily dislodge like a grommet might.
 
I'd also add that chances of a back box becoming live in NI are significantly lower than in GB as there are few circumstances where cable sheath will be in contact with entry point of box. Cables buried in walls are enclosed in conduit and those in stud walls generally enter boxes through a PVC female adaptor that won't easily dislodge like a grommet might.
You may find the same sort of spark that doesn't fly lead may also not bother with grommets and say It's absolutely fine.
 
You may find the same sort of spark that doesn't fly lead may also not bother with grommets and say It's absolutely fine.

I've no idea what practices are engaged in GB, but even the most careless spark in NI will ensure cables are suitably protected upon entry to metal boxes and seldom with a flimsy grommet.

The last time grommets were in widespread use for that purpose was back in the days of VIR (which was encased in oval metal conduit when buried). Later installations used oval PVC conduit and this was brought into back boxes. Modern installations used round conduit, either brought into boxes or finshed with an adaptor. Metal boxes in stud walls generally have a PVC bush for entry. This isn't just 'good practice', it's the only acceptable practice here. As such, the chances of a back box becoming live are exceptionally low.

Edit: the point I'm driving at is that one person's idea of good practice can be considered appalling by another. While it may indeed be good practice to have a flylead in metal boxes, it isn't necessarily a requirement and would appear to be the least of issues on the OP's list.
 
Last edited by a moderator:
I've no idea what practices are engaged in GB, but even the most careless spark in NI will ensure cables are suitably protected upon entry to metal boxes and seldom with a flimsy grommet.

The last time grommets were in widespread use for that purpose was back in the days of VIR (which was encased in oval metal conduit when buried). Later installations used oval PVC conduit and this was brought into back boxes. Modern installations used round conduit, either brought into boxes or finshed with an adaptor. Metal boxes in stud walls generally have a PVC bush for entry. This isn't just 'good practice', it's the only acceptable practice here. As such, the chances of a back box becoming live are exceptionally low.
The thing that peeves me is that a lack of grommets or indeed lack of fly lead will get noted or may even pick up a c3 by the same sparky I've seen not use them.
 
It's not good practice, either.

Not all light switches have an earthing ring.

I would rather fit a fly lead as there is always the chance of the back box becoming live.
You could say that's a matter of opinion....and depends on the state of the
the installation anyway, especially termination wise.
It's a simple topic with loads of consequential 'ifs and 'if nots'.
 

Reply to Is this a Part P failure? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
379
  • Question
So this was resolved. I used a line tester to see if I had power across the breaker on the main box in the house. Breaker tested fine. Then I...
Replies
3
Views
1K
  • Question
Live wires under floorboards? any years ago, when my daughter was just a crawling stage, we were having a new carpet fitted in an upstairs room...
Replies
9
Views
799
And if it's a garage then use metal clad accessories.
Replies
5
Views
353
  • Question
Perhaps it's no longer economically viable to produce elements for this oven and they decided to supply something that would work with slight...
Replies
9
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks