Hello everyone,
I would be happy to hear your opinion about wiring RCBO inside switchboboards, panels. Here I attached some example.
We have 9 (F1-F9) RCBOs, each 20A. If we connect first one (F1) with 16mm2 wire to first phase busbar, second (F2) with 16mm2 to second phase busbar and third (F3) with 16mm2 to third busbar, and neutral with 16mm2 to F1:N, then we can connect everything with comb busbar (L1/N/L2/N/L3/N/L1/N...). Because first phase wire (16mm2) will be enough to supply all first phase RCBOs (F1,F4,F7), 3x20A=60A which is OK for 16A wire. But, what is with neutral wire? The neutral wire in such situation will be undersized? Neutral is the same for
all RCBOs (9 total)....In such way, It looks that we can connect only 3 RCBOs with one comb busbar, because 3X20A is 60A for neutral wire...I would like to hear your opinion..
I would be happy to hear your opinion about wiring RCBO inside switchboboards, panels. Here I attached some example.
We have 9 (F1-F9) RCBOs, each 20A. If we connect first one (F1) with 16mm2 wire to first phase busbar, second (F2) with 16mm2 to second phase busbar and third (F3) with 16mm2 to third busbar, and neutral with 16mm2 to F1:N, then we can connect everything with comb busbar (L1/N/L2/N/L3/N/L1/N...). Because first phase wire (16mm2) will be enough to supply all first phase RCBOs (F1,F4,F7), 3x20A=60A which is OK for 16A wire. But, what is with neutral wire? The neutral wire in such situation will be undersized? Neutral is the same for