During EICR found this at wall lights, would you code this, these lights did not offer a great termination option[ElectriciansForums.net] Wall light connections any code
 
Don’t think I would even note it, when the light is against the wall, the internal cores are not exposed until inside the fitting.
 
class II fitting? Why does the cpc not enter the fitting?
[ElectriciansForums.net] Wall light connections any code
These are the lights awful to connect… onto a plastic lamp holder fixed onto the fitting..cpc bent over & not going into fitting…they are Class II …most Probably just a note on the EICR just saying not ideal
 
Just open at top? Not behind glass?

So basic insulation not within an enclosure?

Rubbish design, but somehow it passes

Great for collecting dead bluebottles.
 
Just open at top? Not behind glass?

So basic insulation not within an enclosure?

Rubbish design, but somehow it passes

Great for collecting dead bluebottles.
Yea open design we wouldn’t connect this… these days..but like all says the insulation unsheathed is behind hidden by the fitting
 

Reply to Wall light connections any code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
820
It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top