I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I am a layman.

The wiring is approx 30. Years old. 4 circuits, 2 x lights, one mains (incl kitchen), one for living room.

We will be renovating the ground floor of the property including the kitchen.

Observations
  • no RCD protection to any circuit (C2)
  • Damage to electrical wiring accessories (C2)
  • Burnt connections in the back of kitchen sockets (possible cause of overloading or loose connections) (C2)
  • immersion heater has been rewired on the same circuit as the sockets - risk of overloading (C2)
  • no CPC continuity to circuit 2 ring main (F1)
  • unable to locate water bonding (F1)
  • no smoke alarms (C3)
  • no surge protection fitted to consumer unit (C3)

The sections of the report on the EICR as C2 are
  • 4.13
  • 4.17
  • 4.18
  • 5.3
  • 5.5
  • 5.12
  • 5.18
  • 6.1

Thank you
 
Can you post the whole report here, but remove the name of the company that did the inspection?
There's a best-practise guide from electrical safety first called best practise guide 4 that is worth you acquiring.

Generally wiring from 30 years ago would normally be in serviceable condition. The full report should help us gain a better picture. The reasons for requiring a rewire are usually
a) dangerous wiring that is at end of life or has been damaged. Some of the tests on the report will help determine this
b) not enough points in the right places or not enough circuits to cope with modern demands
c) revonations are happening and it's a good opportunity

Quick thoughts about the other items:
  • no RCD protection to any circuit (C2) See Best Practise Guide 4
  • Damage to electrical wiring accessories (C2) Not expensive to replace
  • Burnt connections in the back of kitchen sockets (possible cause of overloading or loose connections) (C2) If the wiring is serviceable the accessories can be changed.
  • immersion heater has been rewired on the same circuit as the sockets - risk of overloading (C2) This is a reasonable comment in my view.
  • no CPC continuity to circuit 2 ring main (F1) This should be a C2, FI would be for if he couldn't complete the test. This needs sorting out.
  • unable to locate water bonding (F1) The water pipes can be tested to see if it is likely they are bonded.
  • no smoke alarms (C3) This should be a NOTE as it doesn't relate to electrical safety.
  • no surge protection fitted to consumer unit (C3) Fair enough
 
Can you post the whole report here, but remove the name of the company that did the inspection?
There's a best-practise guide from electrical safety first called best practise guide 4 that is worth you acquiring.

Generally wiring from 30 years ago would normally be in serviceable condition. The full report should help us gain a better picture. The reasons for requiring a rewire are usually
a) dangerous wiring that is at end of life or has been damaged. Some of the tests on the report will help determine this
b) not enough points in the right places or not enough circuits to cope with modern demands
c) revonations are happening and it's a good opportunity

Quick thoughts about the other items:
Thank you - I attach the report below.
 

Attachments

  • [ElectriciansForums.net] Help Understanding EICR
    F553ADA8-B22E-46CE-A201-0262E54FBC9E.jpeg
    264.6 KB · Views: 116
  • [ElectriciansForums.net] Help Understanding EICR
    B9E87560-FDB1-446F-8E47-441FD19BF2F9.jpeg
    254.7 KB · Views: 94
  • [ElectriciansForums.net] Help Understanding EICR
    F0CC31F7-877A-45BE-BB5F-BEE226D10C34.jpeg
    435.9 KB · Views: 85
  • [ElectriciansForums.net] Help Understanding EICR
    468DE5DE-4341-4C63-9649-6A01F1F99435.jpeg
    716.5 KB · Views: 86
  • [ElectriciansForums.net] Help Understanding EICR
    FD3B11CA-28C3-4F64-8B9D-F3BC39E7FB36.jpeg
    833.5 KB · Views: 68
  • [ElectriciansForums.net] Help Understanding EICR
    DD6387DA-E6E2-4BC6-B762-F555125BDE32.jpeg
    581.4 KB · Views: 113
Hmmm. Well he can't have it both ways - his test results actually portray the fixed wiring as being in excellent condition. (The insulation resistance tests for all circuits are all >200M.). If the overall condition is as bad as he says I'd be very surprised to get those readings. The discrepancy between the overall comments and the test results make me wonder if those tests actually happened or the readings were invented.

I also noticed 4.17 - RCD's required for fault protection. This should not be a C2. Fault protection is covered by other methods on your installation and the tests results show it will work. I worry when I see this as it doesn't build confidence.

Also, he's listed type AC RCD protection for each circuit. This is very confusing.

So far, at a minimum and obviously without seeing it I'd be saying that
-the upstairs socket circuit needs fixing
-some accessories may need changing
-a new circuit should be run for the immersion heater
I'd also be advising a new consumer unit is installed but that doesn't mean what is there isn't safe. It's just that modern units do lots more to protect people from the dangers of electricity.

Additionally the insulation resistance results need confirming (ideally by someone else) as you are relying on them to know whether the opportunity should be seized to get some new cables in. This is really the most important thing. If we believe those results I'd struggle to justify a rewire for safety reasons.

As I already wrote - it might be that your intended use of the property means there are insufficient points and a rewire would be a good idea for other reasons.
 
Thank you - all advice greatly appreciated. The intended power points are adequate for what we need.
We will be fitting a new kitchen - would that change anything? Apologies I am a complete novice.
Attached the consumer unit (aware this needs replacing as a minimum)
 

Attachments

  • [ElectriciansForums.net] Help Understanding EICR
    77DB5249-C364-4F71-A19F-4AA545ACFAA6.jpeg
    956 KB · Views: 103
Hmmm. Well he can't have it both ways - his test results actually portray the fixed wiring as being in excellent condition. (The insulation resistance tests for all circuits are all >200M.). If the overall condition is as bad as he says I'd be very surprised to get those readings. The discrepancy between the overall comments and the test results make me wonder if those tests actually happened or the readings were invented.

I also noticed 4.17 - RCD's required for fault protection. This should not be a C2. Fault protection is covered by other methods on your installation and the tests results show it will work. I worry when I see this as it doesn't build confidence.

Also, he's listed type AC RCD protection for each circuit. This is very confusing.

So far, at a minimum and obviously without seeing it I'd be saying that
-the upstairs socket circuit needs fixing
-some accessories may need changing
-a new circuit should be run for the immersion heater
I'd also be advising a new consumer unit is installed but that doesn't mean what is there isn't safe. It's just that modern units do lots more to protect people from the dangers of electricity.

Additionally the insulation resistance results need confirming (ideally by someone else) as you are relying on them to know whether the opportunity should be seized to get some new cables in. This is really the most important thing. If we believe those results I'd struggle to justify a rewire for safety reasons.

As I already wrote - it might be that your intended use of the property means there are insufficient points and a rewire would be a good idea for other reasons.
Thank you - in terms of estimated costs (or is it a case of how long is a piece of string) would you expect?
 

Reply to Help Understanding EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
430

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top