Hey guys,

looking for a bit of advise on the installation of an outside light.

I plan on chasing out the plasterboard and running a cable from a spare light switch in the kitchen through to the exterior (approx. 4.5m away).

The light I have seen is: LAP Weyburn Outdoor LED Floodlight Black 50W 5000lm - Screwfix - https://www.NoLinkingToThis/p/lap-weyburn-outdoor-led-floodlight-black-50w-5000lm/671pg

I currently have some 2.5mm grey twin and earth. The light itself is .75mm cable. Do I need to get some 1.5mm or .75 cable instead? It looks like all the existing circuits are 1.5mm. The circut is protected on a 6a mcb.

Secondly, what is the best way to connect, can i use Wago connectors / terminal block and push in to the cavity, or is it best to use an interior junction box in the wall and connect the flex from the light internally?

thanks,
 
it does have RCD protection of 6a at the consumer unit.

For the sake of clarity could you post a picture of this?

If its rated at 6A then its and MCB not an RCD. But it may be an RCBO which is a device that combines an MCB and an RCD in the same unit.

It is very important to ensure that the circuit has the correct 30mA RCD protection as this is a requirement of the wirkng regulations and provides you with protection against electric shocks.
 
For the sake of clarity could you post a picture of this?

If its rated at 6A then its and MCB not an RCD. But it may be an RCBO which is a device that combines an MCB and an RCD in the same unit.

It is very important to ensure that the circuit has the correct 30mA RCD protection as this is a requirement of the wirkng regulations and provides you with protection against electric shocks.

Please see attached consumer unit. Ground floor lighting is protected.

thanks :)
 

Attachments

  • [ElectriciansForums.net] Installation of Outdoor Light
    Consumer.jpg
    45.6 KB · Views: 75
Post a pic of the wires at the switch? They may not necessarily be neutral, they could be live I.e a switched live that has not been sleeved in the correct colour. Make sure you switch the circuit off before removing the switch cover though in case any connections are loose.
 
Post a pic of the wires at the switch? They may not necessarily be neutral, they could be live I.e a switched live that has not been sleeved in the correct colour. Make sure you switch the circuit off before removing the switch cover though in case any connections are loose.
Hi,

the wires arent switched neutrals. I purely need advice on cable size and connecting the 0.75 to internal wire.

thanks,
 
1.0 or 1.5 T&E from switch to light.
Outside waterproof jointbox onto the flex

Safe zones. You can go straight up from the switch, but it is very likely you will find the cables feeding this switch buried in the wall
 
Hey guys,

looking for a bit of advise on the installation of an outside light.

I plan on chasing out the plasterboard and running a cable from a spare light switch in the kitchen through to the exterior (approx. 4.5m away).

The light I have seen is: LAP Weyburn Outdoor LED Floodlight Black 50W 5000lm - Screwfix - https://www.NoLinkingToThis/p/lap-weyburn-outdoor-led-floodlight-black-50w-5000lm/671pg

I currently have some 2.5mm grey twin and earth. The light itself is .75mm cable. Do I need to get some 1.5mm or .75 cable instead? It looks like all the existing circuits are 1.5mm. The circut is protected on a 6a mcb.

Secondly, what is the best way to connect, can i use Wago connectors / terminal block and push in to the cavity, or is it best to use an interior junction box in the wall and connect the flex from the light internally?

thanks,
 
Firstly, you would NEED a neutral at the switch (not just a blue or black wire, which is likely a switched live).
Second: You need to run the concealed wire under the plasterboard in a "prescribed zone" (e.g. vertically or horizontally) AND it will need 30mA RCD-protection.
Third: 2.5mm is TOO BIG! (It may not fit in either the light or the switch box). 0.75mm (flex) isn't recognised by BS7671 (and flex wire is frowned upon for fixed installation), BUT 1.0mm Twin and Earth is fine - unless exposed to sunlight, in which case it is NOT OK! A different wire, or conduit, will be needed (although painting the wire, arguably, could provide the required UV protection!)
Fourth: You should ensure the Earth wire is fully functioning (even though the new light may not require it).
Wago connectors, or similar, OR choc blocks are fine for extending the Neutral and Earth (the Live will come from the switch).

Unless all of the above can be assured, I would advise you employ an electrician.
 
BS7671 2022
Table 52.3: Lighting and Power circuits: min 1.0mm

521.9.1: A flexible cable shall be used for wiring only when the relevent provisions of BS7671 are met (i.e. see above).
Flexible cables used for fixed wiring shall be of the heavy duty type unless .....

So minimum 1.0mm heavy duty, or protected against mechanical damage.
(Perhaps not "frowned upon" but used conditionally! Easier to advise a non-electrician that it isn't the perfect choice)
 

Reply to Installation of Outdoor Light in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3
Replies
68
Views
4K
Yes, I realised the best thing would be to just fit a floodlight (LAP Weyburn Outdoor LED Floodlight Black 20W 2000lm - Screwfix -...
Replies
5
Views
1K
  • Question
It depends on the type of Earth, but as long as >6A fault current can flow from L to E, it can still trip an MCB! But as stated above, it is...
Replies
15
Views
5K
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
873
Hi all, I have a couple of questions I'm hoping you can help with. I have put a solar panel on my kids play house which charges a 12v battery. I...
Replies
0
Views
299

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks