I found a picture online of a standard UK connection in a block of flats.

Where I have circled blue, would those earth clamps around the orange cable somehow cut into the neutral wire to connect within the orange sleeving?

Or are they just clamped to the sleeve for some arbitrary reason?

[ElectriciansForums.net] Are these earth wires connected to neutral?
 
No, there is no connection to neutral at those clamps.

The cable is mineral insulated copper sheathed, with an orange PVC oversheath. The copper sheath is what gives the cable its overall form and strength and served as the CPC of the cable, but it isn't visible in the pic because it's covered by the orange PVC oversheath. Cuts have been made through the PVC to allow the clamps to connect to the copper sheath. Inside the sheath, the solid copper line and neutral conductors are insulated with magnesium oxide powder, which is sealed at the ends to prevent moisture ingress.

However, this picture shows very bad installation practice. MICC should not be installed and terminated in this way. The glands at the top of the cables should be mounted into an earthed metal enclosure which would make the connection to the sheath and enclose the tails emerging from the seals, which have only basic insulation and should not be exposed. It would also support the cables and prevent them hanging from the conductors as they are seen doing here. The concentric cables connected to the top of the cutouts are shoddily installed too.

In a nutshell, don't learn anything from this one.
 

Reply to Are these earth wires connected to neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3
Replies
68
Views
4K
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
871
  • Question
Responsibility is with whoever made final connections at the shower. The person that tested the supply at the shower has likely got those readings...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks