Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the requirements disconnection as ADS under earth fault conditions and the adiabatic equation as reg 543.1.3."
Circuit: Single core pvc 70* 2.5mm2 + 2.5mm2. 16A Type B 61009-1
r1+r2 = 0.22
Ze = 0.11
Zs = 0.23
Pfc = 230/0.23 = 1000A
Square root of 1000 squared x 0.1 = 316.227
316.227/k(115) = 2.749
So 2.5mm is undersized? Should I be calculating a different way with let through energy or leave it as and use a 4mm?
Thanks!
Circuit: Single core pvc 70* 2.5mm2 + 2.5mm2. 16A Type B 61009-1
r1+r2 = 0.22
Ze = 0.11
Zs = 0.23
Pfc = 230/0.23 = 1000A
Square root of 1000 squared x 0.1 = 316.227
316.227/k(115) = 2.749
So 2.5mm is undersized? Should I be calculating a different way with let through energy or leave it as and use a 4mm?
Thanks!