liebfraumilch
DIY
The black unit in the middle is the time switch that enables the Off Peak fuse board for the heaters and water.
It's switched at the times shown, E.7, or should be, by a Radio signal put out on BBC transmitters.
They were originally mechanical timeswitches but changed to this unit, then to timeswitches built into the meter.
The radio signal is being turned off sometime next year so that's probably why you're going to a "Smart Meter".
If the off peak water heater is coming on then the off peak heaters , if switched on must be.
Bristol Energy or their subcontract meter fitters / meter leasing company should be removing the black teleswitch and using a 5 wire "Smart Meter" that will also do the switching for Off Peak.
Hello snowhead,
Just want to report back that after 4 weeks of hassle we've managed to go from a traditional meter to a "smart" meter.
Indeed the black teleswitch has been replaced by a 5-wire meter.
Interestingly enough, this has not fixed our original problem; that OFF peak circuit is still on during daytime under a E7 tariff.
The installer was quick enough to show us that the 5th cable is constantly live (the one on the right.) Hence no time switching happens.
How does this happen? Any idea who we should speak to?