PAT testing a Ariston Andris under sink water heater | on ElectriciansForums

Discuss PAT testing a Ariston Andris under sink water heater in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

punkin

-
Joined
Nov 19, 2012
Messages
30
Reaction score
14
Location
sheffield
Hi All

I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix - https://www.screwfix.com/p/ariston-andris-lux-undersink-water-heater-2kw-10ltr/3248g
Its a plugin & I’m trying to PAT test it.
It doesn’t say which class its is under (1 or 2) I would assume it’s a class 1 but when I try the Earth continuity to the pipes going in and out, I get a fail, no continuity to earth whatsoever
Does anyone know if its Class 1 or 2?

Thanks
Pete
 
Ariston undersink water heaters (usually / should) have these fitted at the inlet and outlet.
 

Attachments

  • [ElectriciansForums.net] PAT testing a Ariston Andris under sink water heater
    Ariston.PNG
    238.1 KB · Views: 4
The manual I just found on the Internet shows a requirement for a 3 core supply cable and an earth connection when installing it. Not 100% sure it was exactly the same version though. If the device doesn't have the class II logo on the spec plate then it will not be double insulated and so will be class I.
 
As per DPG, I found by accident an installation manual for the South African model (the wording of the instructions being very similar to the European one except for standards) which has a diagram showing the earth being connected to the metalwork of the immersion heater mounting bracket Inside the unit.
It would seem that to test earth continuity you would have to take the cover off!

[ElectriciansForums.net] PAT testing a Ariston Andris under sink water heater
 
Last edited:
Hi All

I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix - https://www.screwfix.com/p/ariston-andris-lux-undersink-water-heater-2kw-10ltr/3248g
Its a plugin & I’m trying to PAT test it.
It doesn’t say which class its is under (1 or 2) I would assume it’s a class 1 but when I try the Earth continuity to the pipes going in and out, I get a fail, no continuity to earth whatsoever
Does anyone know if its Class 1 or 2?

Thanks
Pete
No bonding to the I assume copper water pipes ?
 
No bonding to the I assume copper water pipes ?
The instructions require you to install the isolating plumbing fittings (post #2) to avoid electrolytic corrosion of the unit!

But yes, I agree, if the pipes are copper and bonded and the unit is connected up you would expect the earth continuity. But that's not a PAT, sorry ITSEE, test!
 
Last edited:
I'm surprised no-one has yet asked the obvious question..... why are you trying to test a non-portable device with a PAT test?
 
I'm surprised no-one has yet asked the obvious question..... why are you trying to test a non-portable device with a PAT test?

Don't forget it's ISITEE, not PAT. It can apply to non portable items as well. And often doesn't involve actual testing. The term PAT is very misleading.
 
Don't forget it's ISITEE, not PAT. It can apply to non portable items as well. And often doesn't involve actual testing. The term PAT is very misleading.
True - however - that's not what the OP stated.
 
PAT testing is no longer a recognised term.
The Code of Practice edition 5 removed all traces of the term.
And that's for precisely the reason raised by @Rockingit, that is, to remove any confusion between what equipment should be tested and/or inspected. ISITEE applies to ALL electrical equipment whether portable or not.
 
Anyone testing equipment for safe use, should also be competent enough to be able to ensure that the supply is also safe.
 
Ariston undersink water heaters (usually / should) have these fitted at the inlet and outlet.
Yes I would have thought so but the fittings on this are slightly corroded. So I would assume the outlet would be insulated like in a shower. I will have to open the thing I reckon for a closer look.
 
As per DPG, I found by accident an installation manual for the South African model (the wording of the instructions being very similar to the European one except for standards) which has a diagram showing the earth being connected to the metalwork of the immersion heater mounting bracket Inside the unit.
It would seem that to test earth continuity you would have to take the cover off!

View attachment 107896
Yep I think I would agree with you, bugger, as you can imagine, I need to disconnect the pipes under the sink and I'm not as flexible as I used to be.
 

Reply to PAT testing a Ariston Andris under sink water heater in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
309
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
290
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top