Inspecting and testing a consumer unit as part of my training and have noticed that the circuit breaker for the SPD is on the RCD? I am unsure weather this is acceptable as I haven't come across this configuration and I am pretty new understanding SPDs could one of you more experienced people explain to me why it is or isn't it would really help with my understanding and training.


[ElectriciansForums.net] SPD on RCD acceptable or not?
 
No, it should not be off a 30mA RCD as it might trip it on a surge.

They are fine after a 'selective' RCD (once common as a TT incomer) as that will ignore short spikes of voltage leading to imbalance current (the sort of thing SPD deal with).
 
No, it should not be off a 30mA RCD as it might trip it on a surge.

They are fine after a 'selective' RCD (once common as a TT incomer) as that will ignore short spikes of voltage leading to imbalance current (the sort of thing SPD deal with).

I just asked one of the people I am training with and they said it was fine as this brand of SPD no earth leakage so can be installed downstream of an RCD/ RCBO. Would this then be fine if he is correct?
 
I hope you also noticed the missing busbar shield and unbalanced load between the two RCDs.

This is an image from screwfix site of that type of board, (BG) where the SPD is through an MCB, not an RCD. I can only assume your board has been retrofitted with an SPD, not original
[ElectriciansForums.net] SPD on RCD acceptable or not?
 
Inspecting and testing a consumer unit as part of my training and have noticed that the circuit breaker for the SPD is on the RCD? I am unsure weather this is acceptable as I haven't come across this configuration and I am pretty new understanding SPDs could one of you more experienced people explain to me why it is or isn't it would really help with my understanding and training.


View attachment 108233
Surge protective devices (SPDs) should wherever possible be installed upstream of RCD to prevent unwanted tripping caused by transient overvoltages


Also 534.4.5.1
 
Last edited:
I just asked one of the people I am training with and they said it was fine as this brand of SPD no earth leakage so can be installed downstream of an RCD/ RCBO. Would this then be fine if he is correct?
The way an SPD works is by diverting the surge to earth. This will cause a trip leaving the surge free to find another route to earth.
Higher quality brands actually spell out that only a selective RCD may be fitted upstream, e.g. Schneider:

[ElectriciansForums.net] SPD on RCD acceptable or not?

The BG spec sheet doesn't talk about coordination of devices, but does confirm my comment:

[ElectriciansForums.net] SPD on RCD acceptable or not?
 
No, it should not be off a 30mA RCD as it might trip it on a surge.

They are fine after a 'selective' RCD (once common as a TT incomer) as that will ignore short spikes of voltage leading to imbalance current (the sort of thing SPD deal with).

This got me thinking; on a TT arrangement with an all RCBO board and no upfront RCD you'd need to provide a suitable RCD for the SPD?

What about boards whose SPDs don't require an MCB for protection presumably they would likely require a suitable RCD for fault protection if installed on a TT supply?
 
This got me thinking; on a TT arrangement with an all RCBO board and no upfront RCD you'd need to provide a suitable RCD for the SPD?

What about boards whose SPDs don't require an MCB for protection presumably they would likely require a suitable RCD for fault protection if installed on a TT supply?
I'm not following your reasoning. Why would you need to provide RCD protection for an SPD?
 
I'm not following your reasoning. Why would you need to provide RCD protection for an SPD?
I think he is considering a L-E fault within the SPD itself not clearing the main supplier fuse.
My understanding is that the construction method makes this virtually impossible.
 
The SPD type for TT have one device L-N and another N-E to reduce the risk of a L-E short needing some means to clear it (e.g. an RCD up-front). Often they are used in most cases due to the 'safe' arrangement.

The SPD designed for TN systems have all devices from live-E but they don't have the same risk of L-E causing a live installation.

Personally, and due to being a bit paranoid (partly my nature, partly the Voice of Experience), I would use a 100mA selective RCD up-front of an all RCBO board just in case, but if properly installed and correct SPD used then it is not absolutely necessary.
 
In the regs they are refereed to as CT1 and CT2, but for a SP system they are often denoted as 2+0 and 1+0 (just to add confusion with Type 1 and Type 2 of course, as we have Type A and Type B RCDs along with B-curve MCB, etc.) or for 3P as 4+0 and 3+1, etc.

See Table 534.5 under regulation 534.4.6
 
In the regs they are refereed to as CT1 and CT2, but for a SP system they are often denoted as 2+0 and 1+0 (just to add confusion with Type 1 and Type 2 of course, as we have Type A and Type B RCDs along with B-curve MCB, etc.) or for 3P as 4+0 and 3+1, etc.

See Table 534.5 under regulation 534.4.6
You bring up an interesting point.
A Fusebox SPD kit has the L-N and N-E configuration and is advertised as suitable for TN and TT earthing systems. So I get quite used to not having to think too much about this topic. It's left me wondering whether any brands in the mid-range domestic market make different devices for TN and TT systems, mainly so I can store away the fact that I need to think if I deviate from Fusebox!
 
I think he is considering a L-E fault within the SPD itself not clearing the main supplier fuse.
My understanding is that the construction method makes this virtually impossible.

I'd be more concerned with ensuring the SPD was suitable for use with TT earthing, than considering an upstream RCD, although it seems that many now are.

Edit: above point covered in significant detail in subsequent posts.
 
I'm not following your reasoning. Why would you need to provide RCD protection for an SPD?

I think he is considering a L-E fault within the SPD itself not clearing the main supplier fuse.
My understanding is that the construction method makes this virtually impossible.
Yes, this was what I was trying think through in my head.
 
You bring up an interesting point.
A Fusebox SPD kit has the L-N and N-E configuration and is advertised as suitable for TN and TT earthing systems. So I get quite used to not having to think too much about this topic. It's left me wondering whether any brands in the mid-range domestic market make different devices for TN and TT systems, mainly so I can store away the fact that I need to think if I deviate from Fusebox!
I think the argument for the 2+0 configuration for the TN-S case is under lighting surge conditions both L & N will both be disturbed by a similar amount w.r.t. E, so clamping both that way keeps the L-N difference down far more than the 1+1 configuration used for TT.

However, for the 1+1 configuration used for TT you get better clamping of L-N voltage for other sorts of disturbances such as fault-clearing or big motors being switched where the underlying surge voltage difference is between L & N anyway.

For TN-C-S is makes little difference given that N & E are tied together typically only a meter or so from the SPD
 

Reply to SPD on RCD acceptable or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
915

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top