Since amendment 2 we only have to carry out the RCD test on 1/2x and 1x. 5x is no longer a requirementWhere is that time stated on the report?
EDIT: It's okay I see it now.
This is the relevant part of the wiring regs isn't it?
Huh, link won't post.
View attachment 108444
So the test results show 54ms at 1x and 23ms at 5x, which as you say are both well within the 300ms (1x) and 40ms (5x) in BS7671.
Thanks
I would question the things that have been mentioned to be only a C3.The test was done 10/08/2021 according to the report, so pre-Amendment 2 (28/03/2022). Although the date doesn't really make sense either because the invoice for the work wasn't charged to the owner until Feb 2022, unless maybe the work was postponed due to lockdown following the initial test?? The reason we're looking at it now is because it's very much only the tip of a larger iceberg.
The thing thatβs probably going to cost you the most is the the fault finding