The new Advance Combi Boiler has a feed from consumer unit using 6mm cable on a 32amp breaker to a 45amp double pole switch. What size cable to the boiler should it be from this switch. It has a fused 3amp supply to the electronics section.
 

Attachments

  • [ElectriciansForums.net] Advance Combi Boiler
    image.jpg
    358.7 KB · Views: 41
  • [ElectriciansForums.net] Advance Combi Boiler
    image.jpg
    376.8 KB · Views: 36
The flex should ideally be the same size as the supply cable, so 6mm.

Plus make sure you use ferrules where required, just a few broken strands on a load like this can be enough to cause a failure.
 

Reply to Advance Combi Boiler in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Article
This is an RSS feed of thread: Changing from system to combi boiler with under floor pipework. Content of the thread: Wondering should i change a...
Replies
0
Views
171
  • Question
If this 6mm T&E cable is independent and straight from the DB. Have a sparky check it’s insulation resistance test…!! ( in case it’s an old cable...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top