On the fiddle ______________ | on ElectriciansForums

Discuss On the fiddle ______________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Judd

-
Joined
Oct 21, 2017
Messages
142
Reaction score
59
Location
Liverpool

Came across this setup today, upon further investigation i noticed the distributors neutral terminal completly slackened off in the meter (looked intentional) is this to prevent any possible current from returning via the meter?
With the 1g switch (just above DB) turned on the meter would read like normal. With the switch off the meter has no neutral and therfore is blank.
 

Came across this setup today, upon further investigation i noticed the distributors neutral terminal completly slackened off in the meter (looked intentional) is this to prevent any possible current from returning via the meter?
With the 1g switch (just above DB) turned on the meter would read like normal. With the switch off the meter has no neutral and therfore is blank.
That needs sorting immediately.

They are using the Earth terminal as Neutral.

The supply to the meter shouldn't be affected unless the Neutral from the cutout was the one loosened ?

I suspect the switch when on is making a path to the N tail out of the meter hence the meter fires up, when the switch is off the meter goes off, but current still flows because of the Earth to Neutral connection.

Eelectricity theft in a very dangerous way.
 
Last edited:
If i've seen right, neutral is coming in, is blocked onto the t+e feeding the switch, which is using the brown as a switching wire for the neutral which then uses bonding cable to act as the main switches neutral?

Do the appliances work when the switch is off?

This is all kinds of whacky, never seen owt like this but it screams 'dead bodies'. Would report this to authorities immediately and would switch the lot off.

I like how they've grommetted their t+e into the board though. That's a conscientious sparky right there.
 
Last edited:
If i've seen right, neutral is coming in, is blocked onto the t+e feeding the switch, which is using the brown as a switching wire for the neutral which then uses bonding cable to act as the main switches neutral?

Do the appliances work when the switch is off?

This is all kinds of whacky, never seen owt like this but it screams 'dead bodies'. Would report this to authorities immediately and would switch the lot off.
I'm guessing it's not the type of meter which stops current flow when not energised.

The silly thing is that they still had to access and disconnect the supply neutral to the meter.
 
What do you mean? Would the neutral from service head to meter not just stay in place in this rig?
If the L and Neutral remained from the cut-out then the meter would be powered whether the o/p tails were connected or not.
 
If the L and Neutral remained from the cut-out then the meter would be powered whether the o/p tails were connected or not.
I'm still struggling to see how this means the meter is registering usage when the 'light' switch is on.

We've got incoming tails, no neutral connected to the meter. Then L out N out of the meter, L goes to main switch, N is switched and goes to main switch via earth bar, which means the circuit must always be using earth as the return since there's no other neutral in the circuit? So when the switch is off, there is basically no actual neutral in the circuit, not in or out of the meter, and there will be a line into the CU and only an earth out, am i getting that right?

Basically would this not function exactly the same without the switched neutral at all?

I've done a sketch of what it looks like to me.

Key:

Mtr - Meter
SH - Service Head
SW - Switch
E - Earth bar
MS - Main switch
 

Attachments

  • [ElectriciansForums.net] On the fiddle ______________
    dodgyCU-min.jpg
    306.9 KB · Views: 22
Last edited:
@rewireIT I think you have it right, the only confusion is over how the meter behaves.
Yes, it would function exactly the same without the switch and the 'N' connection to meter in the sense that all final circuits would 'work'. It's equivalent to doing safe isolation and testing L to CPC bar to confirm polarity.

The point is that the meter (if digital) wont record anything without a return current path. The switch is providing a return current path. So when the switch is on, the meter electronics fire up and records some usage.
 
If the neutral and earth are joined together in the head TNC-S, can this just work as a switch?

Meter neutral supply to CU and Main CPC to CU - normal running conditions and meter functions, if someone hid a crossover switch so now Neutral from the CU then connects to earth and Main bonding cable becomes the neutral tail - I don't think electrically anything would be affected, RCD's etc and anything upstream of the theoretical switch wouldn't care.

If the meter only counts both L+N through it and not L+"Bypass N" Unscrupulous people could wire and hide a free elec / metered elec switch subtlety between the meter and the CU. I'm imagining some sort of rotary switchgear
 
I'm still struggling to see how this means the meter is registering usage when the 'light' switch is on.

We've got incoming tails, no neutral connected to the meter. Then L out N out of the meter, L goes to main switch, N is switched and goes to main switch via earth bar, which means the circuit must always be using earth as the return since there's no other neutral in the circuit? So when the switch is off, there is basically no actual neutral in the circuit, not in or out of the meter, and there will be a line into the CU and only an earth out, am i getting that right?

Basically would this not function exactly the same without the switched neutral at all?

I've done a sketch of what it looks like to me.

Key:

Mtr - Meter
SH - Service Head
SW - Switch
E - Earth bar
MS - Main switch
Diagram looks right to me,
I'm not sure if the meter was 'registering usage' it merely sprang to life.

The conclusion I came to is that the meter must need a neutral terminated 'to it' to operate and read correctly.
 
@rewireIT I think you have it right, the only confusion is over how the meter behaves.
Yes, it would function exactly the same without the switch and the 'N' connection to meter in the sense that all final circuits would 'work'. It's equivalent to doing safe isolation and testing L to CPC bar to confirm polarity.

The point is that the meter (if digital) wont record anything without a return current path. The switch is providing a return current path. So when the switch is on, the meter electronics fire up and records some usage.
Ah great i understand, thanks for that.
 
Diagram looks right to me,
I'm not sure if the meter was 'registering usage' it merely sprang to life.

The conclusion I came to is that the meter must need a neutral terminated 'to it' to operate and read correctly.
Definitely the most wild thing i've seen in terms of a bypass. People usually just henley block and have two separate CU's, one metered and one not, if they want to still record some usage. Can't see any other reason you would have the switch there if you didn't want it registering something.

Mad.
 
If the neutral and earth are joined together in the head TNC-S, can this just work as a switch?

Meter neutral supply to CU and Main CPC to CU - normal running conditions and meter functions, if someone hid a crossover switch so now Neutral from the CU then connects to earth and Main bonding cable becomes the neutral tail - I don't think electrically anything would be affected, RCD's etc and anything upstream of the theoretical switch wouldn't care.

If the meter only counts both L+N through it and not L+"Bypass N" Unscrupulous people could wire and hide a free elec / metered elec switch subtlety between the meter and the CU. I'm imagining some sort of rotary switchgear
How would you stop the neutrals from acting as proper neutrals though since they're all physically connected correctly in the board?

I'm trying to visualise a set up whereby the board can look normal but can be switched to use earth as neutral.
 
Definitely the most wild thing i've seen in terms of a bypass. People usually just henley block and have two separate CU's, one metered and one not, if they want to still record some usage. Can't see any other reason you would have the switch there if you didn't want it registering something.

Mad.
Yes maybe it does register usage so they can just toggle between 'free' and 'paid for' not to arise any suspicion, and/or if any one comes to check everything seems to operate correctly.
 
Yes maybe it does register usage so they can just toggle between 'free' and 'paid for' not to arise any suspicion, and/or if any one comes to check everything seems to operate correctly.
You know from your description of the neutral cut out tail this is exactly what's going on. Head is not in the same location as the board i presume? So if someone comes to read the meter they can toggle the switch and visually the neutral seems to be in the meter.

Can anyone explain now however why this is dangerous? It looks really poor (main neutral essentially switched with 2.5mm) but when actually thinking about it - if the N and E are connected in the head in a TNCS then really isn't this just doing what the head does but in the CU?
 
Last edited:

Reply to On the fiddle ______________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

I have just looked at the wiring diagram on line and there are a lot of internal links which if in the wrong terminal could put 230 volt onto...
Replies
10
Views
767
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
638
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top