What are your thoughts on people wanting to be ultra neat when wiring inside boards? | on ElectriciansForums

Discuss What are your thoughts on people wanting to be ultra neat when wiring inside boards? in the UK Electrical Forum area at ElectriciansForums.net

rewireIT

Esteemed
Joined
Jun 15, 2023
Messages
332
Reaction score
190
Location
Durham
I get wanting to do a good job but does being super neat inside a board really make it a better job?

I don't see any advantage to it aside from aesthetics and if it's something that's not seen then....what's the point in obsessing over how neat it all looks?

To me it's a bit like a kitchen fitter making sure all the feet on his cabinets point the same way even though plinth is going on and covering them all up.

What do you's reckon?
 
The most obvious reason is that it aides future works if each conductor in a circuit is readily identifiable, but there's a vast difference between taking pride in turning out neat work and obsessing over millimetre perfect placement of conductors.

Next would be the ease with which additions can be made - much easier to dress more circuits in a neat board, than negotiating your way through a birds nest.

I don't think the kitchen fitter analogy fits - that's more in line with ensuring plate screws are all oriented the same way, which, ironically, is much more common than fastidiously neat boards.
 
It’s all ended up being a bit of a YouTube beauty contest to some extent

IMO the most important thing is that it’s easy to maintain for the next person… enough slack, tidy correctly ordered conductors etc. this does mean neat, not a rats nest but probably doesn’t have to be quite as “beautiful” as some YouTube examples.
 
[ElectriciansForums.net] What are your thoughts on people wanting to be ultra neat when wiring inside boards?

So would you be happy to test this rats nest that was done a couple of months ago?
And has some obvious faults without looking properly, the original installer wouldn't sign it off and then wouldn't answer the customer's emails calls or texts, mm wonder why!

I was going to attach a picture of one I did a week or so ago for a comparison but it will not have it!

Personally I will always do a neat job of everything I do, it's why I get so much repeat business.
Take pride in your work, do it once and do it properly!
Sy
 
View attachment 109245
So would you be happy to test this rats nest that was done a couple of months ago?
And has some obvious faults without looking properly, the original installer wouldn't sign it off and then wouldn't answer the customer's emails calls or texts, mm wonder why!

I was going to attach a picture of one I did a week or so ago for a comparison but it will not have it!

Personally I will always do a neat job of everything I do, it's why I get so much repeat business.
Take pride in your work, do it once and do it properly!
Sy
Apart from some of the copper conductors being proud of the breakers, there is nothing “wrong” with it.
I agree that it could and probably should be neater but would it make it any safer?

part of me is playing the devils advocate
part of me is thinking conductors in the right holes, screws done up correctly, testing and certification in place, what’s the problem?
 
@James
Neatness wouldn't make it any safer, but.
Hidden in there are some 1.0mm cables protected by 20mcb's and some 2.5mm radial circuits on 32a mcb's.
As well as cables left to fit and not enough spare ways for them.
There are also lighting circuits in with socket circuits it's a bit of a mess, there is also the RCD's maximum allowed leakage to consider, that's a lot of lights and sockets to hang off two RCD's.
And none of it is labeled properly.
I couldn't leave a job I'd done looking like that and walk away a happy contractor!

@freddo
I have no idea why it says that!
 
@James
Neatness wouldn't make it any safer, but.
Hidden in there are some 1.0mm cables protected by 20mcb's and some 2.5mm radial circuits on 32a mcb's.
As well as cables left to fit and not enough spare ways for them.
There are also lighting circuits in with socket circuits it's a bit of a mess, there is also the RCD's maximum allowed leakage to consider, that's a lot of lights and sockets to hang off two RCD's.
And none of it is labeled properly.
I couldn't leave a job I'd done looking like that and walk away a happy contractor!

@freddo
I have no idea why it says that!
Hmm i take all your points and you are right but...does any of that actually get impacted by the wiring not being nice to look at?
 
Neatness and logical routing of conductors can help their identification and tracing and thus purpose which in turn may reduce errors at the time of wiring and later when say inspecting and testing. Neatness also suggests care and pride in a job well done and not rushed to complete.
 
Last edited:
For me I have always viewed doing a consumer unit as the one chance to really show your skills at doing a neat tidy job.
It doesn't have to be perfect but cores cut to a nice length and dressed in neatly , the correct sized sleeving used , tails neatly dressed in etc all make it easier for the next person to work on the board and hopefully keep it neat.
If you start with a rats nest and people add to the rats nests you just end up with a bigger rats nest and eventually your work ends up on here being called a complete rats nest
[ElectriciansForums.net] What are your thoughts on people wanting to be ultra neat when wiring inside boards?
 
I find that RCBO present a problem in being neat due to the connection to the N bus-bar. While not OCD I do like to make sure that visually the cabling in a consumer unit is presented in a way that is crystal clear to anyone following and doing additions or alterations. Being orderly and careful, matching terminal numbers on each circuit et. allows checking on your own work being made much easier. Besides which when EICR comes around and seeing a well wired box inspires (potentially!) the feeling that the installation has been in the hands of someone competent.
Then there is the element of taking a pride in your work, which I think the devil is in the detail. When initially starting out wiring fifty years ago the only test we used to do is megger the installation. Don't tell anyone, we also used to use an incandescent element lamp to test earth by placing L + N then L + E, if the bulb was brighter with the L + E, jobs a goodun! Sorry but that was how it was that long ago. The point being, with such poor testing compared to todays requirements, there was a stong emphasis on terminating and neatnes and being sure that your installation techniques were very studiously executed to obviate a poor megger reading, or any other problems associated with poor connections.
 
View attachment 109245
So would you be happy to test this rats nest that was done a couple of months ago?
And has some obvious faults without looking properly, the original installer wouldn't sign it off and then wouldn't answer the customer's emails calls or texts, mm wonder why!

I was going to attach a picture of one I did a week or so ago for a comparison but it will not have it!

Personally I will always do a neat job of everything I do, it's why I get so much repeat business.
Take pride in your work, do it once and do it properly!
Sy
To be fair that DB/CU looks tight as hell
 
Neatness shows pride and good workmanship in your work. Fault finding a rats nest is a pain in the arse especially on RFC okay the lives are easy but trying to find the legs on N and E when you cant even see the buts of the cable and nothing follows consiquecaly
 
They should make 'untidy' a C2.....that'd teach 'em.

Takes me back to wiping a perfectly good armoured, lead multicore as an apprentice and being patted on the head and told to do it again.
 
Neatness shows pride and good workmanship in your work. Fault finding a rats nest is a pain in the arse especially on RFC okay the lives are easy but trying to find the legs on N and E when you cant even see the buts of the cable and nothing follows consiquecaly
I'm on about being ultra neat though - is there any real difference between 'generally pretty tidy' and 'every single wire is the exact same length and curvature into the termination, i've cable tied all the earths and neutrals together (a hindrance imo)' ?

Is one 'better' than the other? Because i see people slagging work that is completely fine it just doesn't look as pretty.
 
Think how you feel when you take the cover off a board and it's lovely and neat inside.
Compare that to how you feel when it's a rats nest.

I don't really have the time, inclination or ability to make every board look like it belongs on Instagram but I like to think I make a bit of an effort.

I think as long as it's neat and tidy and I've done the best with what I have then it's good enough.

Like it or not the next person in the board will judge your ability based on what they see.
 
I'm on about being ultra neat though - is there any real difference between 'generally pretty tidy' and 'every single wire is the exact same length and curvature into the termination, i've cable tied all the earths and neutrals together (a hindrance imo)' ?

Is one 'better' than the other? Because i see people slagging work that is completely fine it just doesn't look as pretty.

If you're spending time on instagram, chances are most comments will be from people viewing the installation from an entirely aesthetic perspective and many will have no idea what the pretty colours do. Instagram isn't real life and from the little I know about it, the place doesn't even approach real life.

I've never seen anyone cable tie earths together (why would they?) and the only cable tying of neutrals I've seen has been RCBO flyleads which none of us really know how to dress neatly, while maintaining ease of access and identification. The options with neutral flyleads are stark: cable tie, cut short and potentially unable to be moved or do the best you can. If people care for adulation on social media, chances are they're going to make less than pragmatic choices.

This place isn't instagram and, thankfully, represents a wide range of opinions.
 
I do occasioinally see earths and neutrals cable tied in 3 phase boards and that doesn't present any real hindrance - plenty of space to snip them and plenty of space to add or remove cables. What I do hate is people who don't loom incoming circuits when wired in PVC singles - nothing worse than removing a circuit and not being 100% certain the correct earth & neutral are being removed, especially after tracing back some distance through trunking. That sort of laziness is unacceptable, when huge sums of money are involved if the wrong conductor is removed. Perhaps if the people who do this found themselves in the shoes of those who follow behind, they'd be inclined to amend their work ethic - especially when alternative means of verification are nigh on impossible.
 
Like it or not the next person in the board will judge your ability based on what they see.
Why does that matter? Every tradesman ever calls the work of others rough even when it's not.

And again let's keep in mind i'm not saying there's neat then there's rats nest, i'm talking about what's wrong with it being in between - everything identifiable and done correctly but not necessarily good to look at.
 
I do occasioinally see earths and neutrals cable tied in 3 phase boards and that doesn't present any real hindrance - plenty of space to snip them and plenty of space to add or remove cables. What I do hate is people who don't loom incoming circuits when wired in PVC singles - nothing worse than removing a circuit and not being 100% certain the correct earth & neutral are being removed, especially after tracing back some distance through trunking. That sort of laziness is unacceptable, when huge sums of money are involved if the wrong conductor is removed. Perhaps if the people who do this found themselves in the shoes of those who follow behind, they'd be inclined to amend their work ethic - especially when alternative means of verification are nigh on impossible.
What do you mean by loom?
 

Reply to What are your thoughts on people wanting to be ultra neat when wiring inside boards? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I guess my last post was even less direct than intended.
    • Like
Replies
11
Views
591
nicebutdim
N
  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
Replies
15
Views
1K
nicebutdim
N
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
  • Question
Youre in the same boat as me. I was previously with niceic and later on, napit. No issues. I didn't bother finishing my nvq3 as in 2010 during the...
Replies
7
Views
3K
  • Question
If there really is a heaven and a hell and in particular a purgatory I pray every lighting designer spends theirs fitting their own creations...
    • Like
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks