whilst watching many a video in the middle of reading the many books on the journey to becoming a qualified sparky, i notice in a setup, that seems to have multiple main switches and fuses before the distribution board, as i am far from being qualified, let alone experienced, i was wondering if anyone could shed some light on the set-up, more so on the switch/fuse to the bottom right of the picture, as it seems extra, but i have no idea as to why.
[ElectriciansForums.net] wondering about this incoming before the distibution board
 
Last edited by a moderator:
Very simple. The maximum length allowed for the meter tails connection to the consumer unit is 3 metres.
If it is more than that a fuse must be provided to provide over-current protection.
You can’t have 10metre tails only protected by the supplier’s fuse that is in the service head.
 
Very simple. The maximum length allowed for the meter tails connection to the consumer unit is 3 metres.
If it is more than that a fuse must be provided to provide over-current protection.
You can’t have 10metre tails only protected by the supplier’s fuse that is in the service head.
ah, makes sense now, this is only the second time ive seen this set-up, first one being in my mother's bungalow - a 60's build completely re-wired including a new incoming cable all the way back to the overhead line/pole,
 
There was a thread on the Screwfix forum about this a while ago, one poster was going nuts saying the KMF or whatever wasn't necessary, others loved winding him repeatedly saying it was.

I can kind of see his point though, the cutout has a 100A fuse and the KMF might do as well so technically any one of them might blow first in an overload or short circuit scenario. I don't really see what value it adds apart from obedience with the rules.
 
There was a thread on the Screwfix forum about this a while ago, one poster was going nuts saying the KMF or whatever wasn't necessary, others loved winding him repeatedly saying it was.

I can kind of see his point though, the cutout has a 100A fuse and the KMF might do as well so technically any one of them might blow first in an overload or short circuit scenario. I don't really see what value it adds apart from obedience with the rules.
in the case of my mother's home, i think the original distribution board was right at the end of the building in the garage ( in what is now an en-suite bedroom) and the only place to put the new one was daed centre of the building which on the shortest, iagonal route would be around 4 mtrs, but which i assume is 5-6 meters in totall, going off topic - a friend's (retired sparky) friend (a doctor) has had his house recently re-wired, but none of the cabling burried in the wall put through conduit, both of us thinking it should have done, but the sparky doing the work insisting that there's no need for conduit...
 
Dont really need tubing or capping in the wall, plastering over the cable directly is accepted, I always use capping though for a couple of reasons, one its easy to fasten the capping to the wall instead of trying to get a fix on hundreds of clips and two, its a lot easier to replace the cable when someone with half a brain screws or drills though one.

another thing about long tails is if they go through the fabric of the building then they need RCDing as well unless you can get them more than 50mm deep everywhere, so unless you want to start messing about with time delayed RCD's and all that its easier to use a steel wire armour submain instead of tails.
 
I can kind of see his point though, the cutout has a 100A fuse and the KMF might do as well so technically any one of them might blow first in an overload or short circuit scenario. I don't really see what value it adds apart from obedience with the rules.
A properly designed installation would have a lower- rated fuse in the KMF than that in the service head. Otherwise there will be no discrimination.
 

Reply to wondering about this incoming before the distibution board in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top