Hello,

I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may be positioned before or after a RCD but I have always been of the idea that the SPD needs to go before the RCD due to the RCD potentially tripping from a surge leaving the SPD unable to operate correctly.

Can someone please help clear up my confusion on this?



[ElectriciansForums.net] BG SPD after RCD acceptable?
 
Not sure why they have number 7, when number 1 states to connect to a 32A MCB.

I wouldn't connect downstream of an rcd, for the exact reason you mentioned.
Although, i guess there are some situations, where there is a 100mA or time delayed rcd some distance before any consumer unit where the SPD might be fitted....
 
Regulation 534.4.7 covers this, basically the RCD has to have an immunity to surges of at least 3kA and usually that is a selective type (traditionally used as incomers for TT systems, followed by 30mA per circuit (group) for additional protection).

It also advises against fitting a Type 1 SPD after any RCD, and that it might still result in the RCD tripping on a big >3kA surge (with the related issue of loss of healthy circuits).

TL;DR don't do that for RCBO or dual RCD boards.
 

Reply to BG SPD after RCD acceptable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
For anyone interested, I tested the supply side RCBO today and got a 1x I time of <130ms, so I don't believe it is a Type S. I did however have...
Replies
12
Views
3K
  • Question
It is quite a simple process, if you believe a Hazard exists then an Analysis should be done, if at the conclusion of this Analysis this...
    • Like
2 3 4
Replies
84
Views
12K
  • Question
There are some useful and free documents on CU replacement (Best Practice Guide #1) and EICR (Best Practice Guide #4) here...
Replies
16
Views
5K
  • Question
Maybe wonder full pc 1966 or LN with is wonderfull diagrams showing apprentice how it should be done regarding TT to the outer building...
Replies
7
Views
3K
  • Question
other day passed a Shell. £1.59/l sainsburys £1.42/l who's the rip off merchant? atm i do about 150 miles /week, that's 5 gallons in my hiace...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks