Deleted member 155212

Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the future I might need a 7.4kW/32A charging point and the garage isolator is only 60A.

1. Recently, during a kitchen refurb, double pole Mains Isolators were fitted in the Meter Enclosure - image 1. 25mm2 tails were fitted because the incoming power was upgraded to 100A.
2. Inside the garage, opposite the Meter Enclosure, the new tails are connected to an old MEM Isolator Switch - image 2. That Isolator switch has a ceramic re-wirable fuse and that fuse is only rated at 60A.
3. The armoured cable from that MEM Isolator Switch goes to a new, metal, split load Consumer Unit inside the house - image 3. Naturally that Consumer Unit has another Mains Isolator Switch.

The oldest part of the installation is the MEM Isolator Switch. I am having trouble finding a ceramic MEM re-wirable 100A fuse and am not sure that is the best solution anyway. So my questions are:

1. Do I actually need the MEM Isolator Switch in the garage if the Meter Enclosure and the Consumer Unit both have isolator switches?
2. Could that MEM Isolator Switch just be removed OR should it simply be replaced with a 100A cartridge type fuse OR a suitable 100A breaker?
3. One day I will need to fit a Charging Unit for a car and the location of the MEM Isolator Switch would be a good point to take a cable through the garage wall to the outside for that charging point. So what would that arrangement look like? Would it be a very small 'Consumer Type' unit with an isolator switch plus a 32A 'take off' connection for the charging point?
4. OR should the power for that charging point come from the new 'Consumer Unit' inside the house (i.e. the unit in image 3)? It seems odd to take the power all the way to the Consumer Unit in the house and then cable it all the way back to the garage.

Apologies for some of the terminology. Any help and advice would be greatly appreciated. Thanks for your time.
 

Attachments

  • [ElectriciansForums.net] Main Electrics Isolator Switch
    image 1.jpg
    69.1 KB · Views: 204
  • [ElectriciansForums.net] Main Electrics Isolator Switch
    image 2.jpg
    43.4 KB · Views: 58
  • [ElectriciansForums.net] Main Electrics Isolator Switch
    image 3.jpg
    40 KB · Views: 72
I'm guessing the MEM isolator is there because the run to the house consumer unit is more than 3 meters, if it is you need some kind of fuse in between the meter and the consumer unit. You coul dreplace the isolator with a garage type fuse box with several ways, the house being one of them but that would mean the house would be fed from something like a 63A MCB which isn't ideal, even a blowing light bulb could possibly trip it.

The best solution if you want to future proof it is to replace the mem isolator with a tail block,

[ElectriciansForums.net] Main Electrics Isolator Switch


from the tail block go to a new switch fuse isolator that would then supply the SWA for the house and you have spare ways in the tail block to connect a small consumer unit for the car charger and any other electrics in the garage.

[ElectriciansForums.net] Main Electrics Isolator Switch
 
As @oscar21 has said, if the run from the incoming supply to the CU is over 3m then it should have both a means of isolation (now coverd by the supply isolator) and some fault protection (e.g. fuse), as you are not normally allowed to rely on the DNO fuse (in the cut out before your meter) for those.

However, there might be another reason fo it being 60A rated before as that might be the limit of the SWA run to the house CU. In which case if being replaced by a more modern switch-fuse you would also need to limit it to whatever that cable is rated at as well as meeting the disconnection times needed, etc.

Splitting the supply to feed a garage CU that in turn has capacity for the sockets, lights, and an EV charger (without going through the house) is better for various reasons as already suggested.

But this is really not a DIY project! You would be best to get in a professional. It might be someone on this forum is close enough and can help you out.
 
Is the SWA new with the consumer unit upgrade or original, whenever I've seen those older isolators it usually feeds a piece of twin and earth to an old CU, not often a SWA. But if the charger is coming off the tail blocks then you have no reason to upgrade the supply to the consumer unit to 100A anymore, so can leave it at 60A if the SWA isn't big enough. I suppose you could also leave the older isolator there as well if everything complies which it should do if a new consumer unit has just been fitted.
 
The Forum has limited descriptions and the only one applicable was 'DIY' - there is no intention whatsoever to interfere with the arrangement and a qualified electrician will be used.
Good point about the tail block and that will help in all sorts of ways. I will have the SWA checked for rating and the Consumer Unit was fitted very recently.
The tail block will limit the power through the Consumer Unit so maintaining the 60A fuse at the Garage Isolator is a good option.
Thank you all for the valuable comments.
 
The revised arrangement - please check that I have fully understood the points made in the above threads. Obviously a qualified electrician will be used to carryout a detailed survey before any changes are made.
 

Attachments

  • [ElectriciansForums.net] Main Electrics Isolator Switch
    outline plan.jpg
    88.9 KB · Views: 70

Reply to Main Electrics Isolator Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Yes, I was referring to simple installations such as domestic as that is what the thread is about. I also said should rather than must because I...
2
Replies
16
Views
2K
davesparks
D
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top