Hi all,
I've installed a Tesla Gen 3 wall charger supplied by my client.
For your information, the place that I installed is in a block of flat basement where the Meter room is.
After some researching, I've fitted a Proteus board fitted with SPD and PEN fault detection device.
All dead test result is fine. Ze and PFC at the board is fine as well.
Testing with the ev tester, everything goes fine until RCD testing with the tethered socket.
I've set the pp state at 32amp and CP state knob at C, once the mft goes to RCD testing stage, it shows a reading for the dc mA and the charger flashing red light and no power at the tethered lead. The strange thing is the RCD at the board didn't trip.
I've noticed at the app it said that the Ground Fault interrupter is enable, will this affecting the RCD?
I want to know is there any thing that I've done wrong or missed?
Thanks for all the help.
I've installed a Tesla Gen 3 wall charger supplied by my client.
For your information, the place that I installed is in a block of flat basement where the Meter room is.
After some researching, I've fitted a Proteus board fitted with SPD and PEN fault detection device.
All dead test result is fine. Ze and PFC at the board is fine as well.
Testing with the ev tester, everything goes fine until RCD testing with the tethered socket.
I've set the pp state at 32amp and CP state knob at C, once the mft goes to RCD testing stage, it shows a reading for the dc mA and the charger flashing red light and no power at the tethered lead. The strange thing is the RCD at the board didn't trip.
I've noticed at the app it said that the Ground Fault interrupter is enable, will this affecting the RCD?
I want to know is there any thing that I've done wrong or missed?
Thanks for all the help.