Gents,

What is your view from this this clause from BS5266?
[ElectriciansForums.net] Failure of emergency lighting


If you have a lobby with that is part of an escape route that has one fitting, I have never seen an additional fitting being added to satisfy this clause. Even in rooms with two fittings, I have rarely seen both being used as emergency versions??
 
Dees this not have to be looked at in a practical sense? If you have an intermediate escape route lobby 3/4sqm with one light where the entrance door hasn't even closed by the time you open the exit door, putting another emergency light/ exit light here is excessive.

Also a storage/plant room that is 4/5sqm with one fitting? I have never seen an additional emergency fitting put in these rooms
 

Reply to Failure of emergency lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
Replies
15
Views
686
nicebutdim
N
  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N
Hi James, Many thanks for your response and suggestions. The only reservation I have about leaving things as they are and making a contribution...
Replies
2
Views
615
  • Question
Thanks Bennie. Yeah I have Oslo microwave sensor 2D type fittings which I was hoping to use. So permanent supply to all this would suffice? Thanks
Replies
10
Views
1K
  • Question
There's one gotcha with them : if you get one that's been on the shelf a while, you install it, and then 24 later it does it's first full 3 hour...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks