How to install a junction on ring circuit spur? | on ElectriciansForums

Discuss How to install a junction on ring circuit spur? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 19, 2023
Messages
20
Reaction score
2
Location
Ireland
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and the red socket is a spur.

[ElectriciansForums.net] How to install a junction on ring circuit spur?

I need to create a new socket, but the closest socket and the only one I have easy access to is the spur.

Is there any way for me to properly create a socket out of that wiring? I've read somewhere that you shouldn't junction a spur or create a spur of a spur for electrical sockets.

Thanks!
 
Yes. You cannot spur from a spur, but you can introduce a fused connection before the first spur, creating a “fused spur” in which you can have any number of points after the fuse.

Total load of all the spur points is limited to 13A of the fuse.


Does this mean you’ve found the answer to your other thread? Whether it is a ring or a radial?
 
This has bought to mind a quote from the late great Lucien - he once used a phrase that I really liked that cut through all of the complication of normative and informative regs.
He simply said "to be universally recognised as a compliant ring final circuit you shouldn't create a spur from a spur".
That really sums up a complicated situation nicely. As a pedantic detailer I've never liked just saying "Thou shall not" and I've never wanted to try and explain to a non-professional the circumstances under which you can.

To be clear, I'm in agreement that adding a FCU is the best option. I was just in a slightly philosophical mood...

One other thought, is the red socket a single or double?
 

Reply to How to install a junction on ring circuit spur? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Not checked but conductors used for a ring final circuit should be rated no less than 20A therefore any connectors employed should be rated alike.
Replies
10
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Just thinking about every point being a spur off the rfc, and no actual points as part of the rfc….. What if you want to add an additional socket...
2 3 4
Replies
86
Views
7K
  • Question
Been looking at the brochure on Hager over the weekend and trying to work out what I may need. I don't have anything decent to make a wiring...
Replies
4
Views
1K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks