Basically I’ve attended a friend house who asked me to see why his power to his sheds had stopped working. Any help or advice on fixing this mess please
 

Attachments

  • [ElectriciansForums.net] Advice on fixing this outside mess
    IMG_7641.jpeg
    280 KB · Views: 95
  • [ElectriciansForums.net] Advice on fixing this outside mess
    IMG_7642.jpeg
    352 KB · Views: 86
So is RCD tripping?
Obviously cracked box, SWA not earthed this end, and B32 possibly feeding two radials (or is it a RFC?)

All I'd care about is understanding the reason why it doesn't work, and then whether the incoming SWA is sound. IR test it, continuity test it. I'd assume the other end is a fuse or MCB?

Then I wouldn't want to do anything other than start again. From what you've shown I've two instant ideas:
You could fit a little IP65 CU, re-terminate the SWA into that (but earth it), and fit a couple of B16 RCBO's, one for each shed.

Or you could re-terminate the incoming SWA into a galv besa box, or resin joint, extend the SWA and and fit a little garage CU inside the shed.
He could have some lights then as well.
 
So is RCD tripping?
Obviously cracked box, SWA not earthed this end, and B32 possibly feeding two radials (or is it a RFC?)

All I'd care about is understanding the reason why it doesn't work, and then whether the incoming SWA is sound. IR test it, continuity test it. I'd assume the other end is a fuse or MCB?

Then I wouldn't want to do anything other than start again. From what you've shown I've two instant ideas:
You could fit a little IP65 CU, re-terminate the SWA into that (but earth it), and fit a couple of B16 RCBO's, one for each shed.

Or you could re-terminate the incoming SWA into a galv besa box, or resin joint, extend the SWA and and fit a little garage CU inside the shed.
He could have some lights then as well.

Yes the RCD has tripped. It’s feeding two radials of 4mm 3 core NYY to each shed. Which has its own light, socket and FCU. The other end of the cable is a 40a MCB.

I’ve got a Wiska 1010 box and a Vent Plug, if the SWA is no good I may replace with NYY so it’s all the same cable. Would this need to be earthed with an Earth locking nut on that end?

Also replace the connector block with 222 Wago?
 
You don't replace a cable so it matches the other you replace it with a suitable cable. NYY-J does not need an earth lock nut. I'm not sure you are experienced enough to be undertaking such things without supervision.
 
Yes the RCD has tripped.
As bad as that lot looks, the reason could be downstream of there. You need to IR test the two radials in turn.

if the SWA is no good I may replace with NYY so it’s all the same cable. Would this need to be earthed with an Earth locking nut on that end?
Does the SWA have a cable route where it would otherwise need RCD protection at source? You may need to consider this before changing cable type.

Wagos? Yes!
 
You don't replace a cable so it matches the other you replace it with a suitable cable. NYY-J does not need an earth lock nut. I'm not sure you are experienced enough to be undertaking such things without supervision.

What I’m saying is if the SWA is no good. I’m going to replace it with NYY-J Meaning it’s the same cable type used throughout the installation.
 
As bad as that lot looks, the reason could be downstream of there. You need to IR test the two radials in turn.


Does the SWA have a cable route where it would otherwise need RCD protection at source? You may need to consider this before changing cable type.

Wagos? Yes!

The SWA runs into the Garage Consumer unit. It’s on its own MCB. What would be best used to connect the two boxes together. Something like a Brass Compression Gland.
 
Last edited:
So is RCD tripping?
Obviously cracked box, SWA not earthed this end, and B32 possibly feeding two radials (or is it a RFC?)

All I'd care about is understanding the reason why it doesn't work, and then whether the incoming SWA is sound. IR test it, continuity test it. I'd assume the other end is a fuse or MCB?

Then I wouldn't want to do anything other than start again. From what you've shown I've two instant ideas:
You could fit a little IP65 CU, re-terminate the SWA into that (but earth it), and fit a couple of B16 RCBO's, one for each shed.

Or you could re-terminate the incoming SWA into a galv besa box, or resin joint, extend the SWA and and fit a little garage CU inside the shed.
He could have some lights then as well.
Slightly off topic but this has intrigued me for ages, you state "B32 possibly feeding two radials" as that's what it looks like but I don't believe that device has any over current protection at all, its just an RCD with contacts rated to 32A just like the 63A and 80A RCD's we so often see in consumer units.

The bit that intrigues me is why would manufacturers make an RCD that is only rated to 32A when they produce so many that are 63/80/100A rated. what could it possibly be used for that a vastly more common higher rated one couldn't be. All it does is confuse people into thinking its got some kind of over current protection, I'll bet there are hundreds of these devices installed for just that purpose.
 
Slightly off topic but this has intrigued me for ages, you state "B32 possibly feeding two radials" as that's what it looks like but I don't believe that device has any over current protection at all, its just an RCD with contacts rated to 32A just like the 63A and 80A RCD's we so often see in consumer units.

The bit that intrigues me is why would manufacturers make an RCD that is only rated to 32A when they produce so many that are 63/80/100A rated. what could it possibly be used for that a vastly more common higher rated one couldn't be. All it does is confuse people into thinking its got some kind of over current protection, I'll bet there are hundreds of these devices installed for just that purpose.

I've seen quite a few showers which were later additions to installations and fed from a '63A' RCD. Presumably the installer laboured under the misapprehension that this rating represented overcurrent protection.

On your later point I've often wondered if it wouldn't be cheaper for manufacturers to produce only one current rating, rather than a range - 100A being the obvious suggestion. Small 'garage' boards often have an RCD mainswitch rated at 40A. 16A 3ph RCD protected interlocked sockets are often supplied (if indeed an RCD is supplied) with 25A devices. All of these are perfectly acceptable and fit for purpose, but their availabilty suggests there must be a commercial reason for offering a wide range - just not one that is obvious to me.
 
I’ve got a Wiska 1010 box and a Vent Plug, if the SWA is no good I may replace with NYY so it’s all the same cable.

How is the SWA installed and how would your proposed new NYY be installed?

There's a lot more to selecting the right cable for the job than just making it all the same type.

Would this need to be earthed with an Earth locking nut on that end?
Is this a trick question? NYY doesn't have any armour to earth.
 
How is the SWA installed and how would your proposed new NYY be installed?

There's a lot more to selecting the right cable for the job than just making it all the same type.


Is this a trick question? NYY doesn't have any armour to earth.

The SWA goes into the L N terminals on the RCD. It’s then fed into the Garage Consumer Unit on an MCB. Then the Garage has its own feed back to the Consumer unit in the house. It’s currently buried under paving in the garden.

The new NYY-J would be installed in Galvanised Conduit.
 
The SWA goes into the L N terminals on the RCD. It’s then fed into the Garage Consumer Unit on an MCB. Then the Garage has its own feed back to the Consumer unit in the house. It’s currently buried under paving in the garden.

How would the proposed NYY-J replacement be routed back to that consumer unit?
 

Reply to Advice on fixing this outside mess in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

N
  • Article
Help Needed: Fixing My Damaged Tub with Devcon Metal Patch & Fill Hey everyone, I have a pretty messed up tub that I need to fix, and I'm hoping...
Replies
0
Views
217
NETSURFER802
N
ESP - https://www.espuk.com/# is the company you are referring to part of Scolmore
Replies
2
Views
326

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top