Hi guys,

I'm on a job where one of the storage heaters isn't heating up. it is a dimplex model FXL18N 2.34kW.

There are two of these heaters in the property but one is not heating up. I've checked & bypassed the supply using peak supply to verify that electricity is getting into the heater.
At the elements 240v, resistance is 23.7 ohms.

The control / thermostat clicks when moved but no change in resistance at the element & there is no disconnection of electricity when the thermostat is turned to zero. I've duplicated the test at the other heater & exactly the same results.

No thermal trips as there is electricity at the elements live & neutral, can anyone think of anything else i've missed or can try?

Cheers Jon.
 
You might want to be careful doing that - the last storage heater I had to actually fully replace had gone pop because the old boy had pee'd into it. Yep - you read that right! All the internal insulation blanket was sopping wet with urine. That was not a fun job.
I opened it to look at the thermostat. Cut out not open, zero ohms between red and white wires so should get heat. When first turned on seem to be a bit of heat - checked with laser thermomenter with vent open - a few degrees C above ambient then goes cold. Measured resistance between neutral and thermostat output - Megohms. Can these lement fail in such a way theat they heat up a bit and then go open circuit with just a small rise in temperature? Dimplex DXLN
 

Attachments

  • [ElectriciansForums.net] Storage heater not heating up but powered
    dimplex thermostat.jpg
    291.6 KB · Views: 33
Can these lement fail in such a way theat they heat up a bit and then go open circuit with just a small rise in temperature? Dimplex DXLN
Not impossible, but unless it's the smallest version in the range, there are more than one element connected in parallel, so they would all have to fail to get an open circuit reading OR the wiring between the 'stat and the first element has failed..
 
Not impossible, but unless it's the smallest version in the range, there are more than one element connected in parallel, so they would all have to fail to get an open circuit reading OR the wiring between the 'stat and the first element has failed..
Oh Dear - measured the resistance between the neutral of the additional day-time convection heater and live of storage section so no wonder I got open circuit! Before I realised this, I opened up the unit and all elements are ok. Just looked at input section and found the attached - well cooked- no voltage across elements - will replace chock connector and cut off burnt bit of cable. Don't know why was getting small amount of heat on switch on before - perhaps thermostat gone as well.
 

Attachments

  • [ElectriciansForums.net] Storage heater not heating up but powered
    Burnt input block.jpg
    387.4 KB · Views: 28
Oh Dear - measured the resistance between the neutral of the additional day-time convection heater and live of storage section so no wonder I got open circuit! Before I realised this, I opened up the unit and all elements are ok. Just looked at input section and found the attached - well cooked- no voltage across elements - will replace chock connector and cut off burnt bit of cable. Don't know why was getting small amount of heat on switch on before - perhaps thermostat gone as well.

Has anyone known mains cable to go open circuit just from overheating. The wires were completely black when I took them out. Put in new ceramic block and it seems to be working ok now. So elements and thrmostat have lasted 20 years with no problems.
 

Attachments

  • [ElectriciansForums.net] Storage heater not heating up but powered
    New Connector.jpg
    391.2 KB · Views: 24

Reply to Storage heater not heating up but powered in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thought this was sounding a bit familiar. A thread on the same subject from 2021,, There's a link to the manual, but no diagrams, in my post #2...
Replies
23
Views
6K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
478
  • Question
Looks from the circuit diagram that the elements are separate. I'll double check on Monday. Cheers
Replies
2
Views
2K
If you're having new circuits, then a new consumer unit would be highly recommended. One rcd covering the whole installation isn't a good idea...
Replies
2
Views
1K
Thanks, I think you are probably right. I’ll have to get another heater. I was hoping it was going to have two thermal fuses and one had blown...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks