Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason!

Anyway, Table I1 in the OSG says the mΩ/m value for copper with a CSA of 25mm2 is 0.727. However, when I calculate the R value using the formula:
[ElectriciansForums.net] Why don't values in the OSG table I1 match those calculated?
I get 0.688... Does anyone know why the values aren't the same?

Thanks Connor
 
The conductivity value stated on Wikipedia, etc, will be for pure crystal copper, not the annealed stuff with traces of oxygen and other elements used for power cables. I'm not sure if that is enough to explain the difference, but in any case for design work you should use the figures from the cable manufacturing standards, which as @Timbo points out, as the figures that count in the regulations.
 

Reply to Why don't values in the OSG table I1 match those calculated? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top