EICR Test Unsat-Thoughts? | on ElectriciansForums

Discuss EICR Test Unsat-Thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 9, 2024
Messages
7
Reaction score
0
Location
Hull
Good day. First time poster.


We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the circuits checked. Prior to this I inspected as much of the ciruits as possible and checked the sockets, lights for possible issues, it all looked fine with my limited knowledge, apart from the upstairs lighting with the old ALU wiring. We also have the documents from the previous oweners who had the kitchen, cooker and downstairs sockets/lights rewired during building works in 2014, so the 1950/1960s wires are no longer in those ciruits.


The only 1950's wiring is in the upstairs lighting ciruits, the sockets (upstairs) also appear to have been rewired (evident as there is twin and earth PVC).

I was surprised to find that the electrical inspectors only recomendation was a full house rewire based on not a C2 or C3 code for the upstairs lighting, but rather an F1? The only C2 were for No RCD and CU has an unused opening exceeding IPx4 etc. However, the the F1 states - " insulation resistance testing below required valve [for current editon]".


Now I know that the values are low and below the specification, but does this seriously require a full rewire? I can not believe there can not just be a rewire of the upstairs circuit?


To the best of my knowledge, we have items that could have affect the readings also- we have USB plug sockets and I am pretty sure he didn't disconnet all electrical items, I found he left my PC, laptop and other protected items plugged in during testing!


Any thoughts would be greatly appreaciated?
Jim
 
The reason for these "low" readings needs to be established.
Can we see the full report with personal details redacted.
Attached.

Best wishes

Jim
 

Attachments

  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164819.png
    121 KB · Views: 72
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164830.png
    190 KB · Views: 63
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164907.png
    322.5 KB · Views: 65
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164928.png
    385.5 KB · Views: 63
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164957.png
    276.1 KB · Views: 65
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164941.png
    169.8 KB · Views: 59
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-164842.png
    57.7 KB · Views: 63
  • [ElectriciansForums.net] EICR Test Unsat-Thoughts?
    Screenshot_20240109-165446.png
    91.1 KB · Views: 68
It is a leap of faith to suggest it needs rewiring without knowing the cause of the readings. The readings are so low I am wondering whether the lighting circuits have interconnected neutrals and when testing they only disconnected the neutral for the circuit under test but that would need verifying.
They failed to identify the odd ring final continuity readings for circuit 2.
 
It is a leap of faith to suggest it needs rewiring without knowing the cause of the readings. The readings are so low I am wondering whether the lighting circuits have interconnected neutrals and when testing they only disconnected the neutral for the circuit under test but that would need verifying.
They failed to identify the odd ring final continuity readings for circuit 2.
Many thanks.

From you comment, I guess it's best to have it tested by a different engineer?
 

Reply to EICR Test Unsat-Thoughts? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
625

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top