Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading | on ElectriciansForums

Discuss Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Jun 8, 2022
Messages
19
Reaction score
3
Location
Scotland
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained was 0.97 Ohms and 27Amps Pfc.
Now the earthing system itself is quite strange. Next to the consumer unit is an old service head holding a 60A BS 88 fuse. Terminated into this is a 16mm split concentric. The live is connected into the service head and the neutrals go into a henley block. This block is where the 16mm earth going into the consumer unit is connected. The earths of the split concentric are cut off where cable is stripped for termination into the service head.
Things now get interesting.
Outside there is a meter box that the split concentric goes back to. This meter box is supplied by a 16mm 3 core SWA that travels 300+ yards underground from a new box on the edge of a field that was fitted by the SSE last year when new overheads were run to the farm.
This 16mm SWA supplies TWO! cottages. The brown core is the Live for the cottage i was in, the Black is the Live for a cottage next door and the Grey is the Neutral. The sheath of the SWA is the earth. The cores of the SWA go into blocks where they are split and each is then terminated into a switched fused isolator serving the split concentric feed to each cottage. The earths that were cut off at the service head inside the cottage - at this end are connected to the earthing terminal of the switch fuse isolator.
The readings in the cottage for the EICR were generally all ok and under the max Zs value however one ring circuit was measuring at 1.55 ohms. I imagine i could change the RCBO serving this circuit from a 32A to a 20A.
Does anyone know of what should be done here regarding the Ze exceeding the max value? Somewhat in disbelief that two cottages are supplied such a distance with a cable so small!
Thanks[ElectriciansForums.net] Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading
 
Last edited by a moderator:
You can consult the supplier but as to what you can do about it, very little. I assume this is a TN-S supply where the suggested Ze should not exceed 0.80 but this is not an absolute requirement.
 
Did you take a line to neutral loop reading?
The earth clamp isn't ideal they shouldn't be used on cables unless there is something to stop it crushing the cable.
 
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained was 0.97 Ohms and 27Amps Pfc.
Now the earthing system itself is quite strange. Next to the consumer unit is an old service head holding a 60A BS 88 fuse. Terminated into this is a 16mm split concentric. The live is connected into the service head and the neutrals go into a henley block. This block is where the 16mm earth going into the consumer unit is connected. The earths of the split concentric are cut off where cable is stripped for termination into the service head.
Things now get interesting.
Outside there is a meter box that the split concentric goes back to. This meter box is supplied by a 16mm 3 core SWA that travels 300+ yards underground from a new box on the edge of a field that was fitted by the SSE last year when new overheads were run to the farm.
This 16mm SWA supplies TWO! cottages. The brown core is the Live for the cottage i was in, the Black is the Live for a cottage next door and the Grey is the Neutral. The sheath of the SWA is the earth. The cores of the SWA go into blocks where they are split and each is then terminated into a switched fused isolator serving the split concentric feed to each cottage. The earths that were cut off at the service head inside the cottage - at this end are connected to the earthing terminal of the switch fuse isolator.
The readings in the cottage for the EICR were generally all ok and under the max Zs value however one ring circuit was measuring at 1.55 ohms. I imagine i could change the RCBO serving this circuit from a 32A to a 20A.
Does anyone know of what should be done here regarding the Ze exceeding the max value? Somewhat in disbelief that two cottages are supplied such a distance with a cable so small!
Thanks
The maximum permitted Zs for any final circuit with a 30ma 61009 or 61008 device at its origin is 1667 ohms, so the Zs on your ring circuit is satisfactory on a 32a rcbo.
 
Did you take a line to neutral loop reading?
The earth clamp isn't ideal they shouldn't be used on cables unless there is something to stop it crushing the cable.
Hi, yes i believe my reading was the same between line and neutral. Yeah it would have been better if whoever installed this had brought it into an enclosure and used an earthing nut or something else more appropriate.
 
You can consult the supplier but as to what you can do about it, very little. I assume this is a TN-S supply where the suggested Ze should not exceed 0.80 but this is not an absolute requirement.
I should correct myself, it is a 32A mcb with an 80A type A rcd fitted at the c/u. Also the box in the field where the 16mm SWA originates appears to show the system as TNCS as SSE have the earth coming out of their service head.
 
The maximum permitted Zs for any final circuit with a 30ma 61009 or 61008 device at its origin is 1667 ohms, so the Zs on your ring circuit is satisfactory on a 32a rcbo.
Hi, isn't the 1667 ohms reading only for Type S RCD's? in page 70 of the regs i see that value in a table. regarding S type?
 
I should correct myself, it is a 32A mcb with an 80A type A rcd fitted at the c/u. Also the box in the field where the 16mm SWA originates appears to show the system as TNCS as SSE have the earth coming out of their service head.
Fault protection is still provided by the RCD.
If it is TN-C-S then the armour of that cable is inadequate to support main protective bonding.
 
Fault protection is still provided by the RCD.
If it is TN-C-S then the armour of that cable is inadequate to support main protective bonding.
Perhaps i should suggest to the farmer an earth spike should be installed at the meter box beside the two cottages in order to provide an adequate earthing arrangement?
This is where the SWA terminates into the box 300 yards away. Don't you think that the cable size is massively underrated for the distance?[ElectriciansForums.net] Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading
 
Last edited by a moderator:
It is certainly undersized by some way but they are not necessarily working to the requirements like us. I would question it and see their response.
 

Reply to Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top