Hi
I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an armoured down the wall, in a 600mm deep trench and then up the wall of the outbuilding. I've marked the originally intended route on the image below, which also shows just how close the two are.
However when the area was being dug out to prep for the concrete base I found a thick cast iron pipe running parallel to the back wall of the house, this was buried very shallowly, see the two pictures below.
A call to SGN (my local gas network supplier) and a visit from one of their engineers confirmed that this is a gas main that feeds both my property and that of my neighbour. The engineer had a diagram which shows the line runs from the road, down my driveway, along the side of the house before turning across the rear. See the dodgy MS Paint diagram below.
I was told by the SGN engineer that I was not to disturb the pipe under any circumstances, so digging under it to run the armoured isn't an option. The property is a bungalow, so running a cable across on a catenary isn't viable either.
I'd like to know what would be a reasonable approach to getting a cable run in a compliant manner - any help or advice appreciated.
I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an armoured down the wall, in a 600mm deep trench and then up the wall of the outbuilding. I've marked the originally intended route on the image below, which also shows just how close the two are.
However when the area was being dug out to prep for the concrete base I found a thick cast iron pipe running parallel to the back wall of the house, this was buried very shallowly, see the two pictures below.
A call to SGN (my local gas network supplier) and a visit from one of their engineers confirmed that this is a gas main that feeds both my property and that of my neighbour. The engineer had a diagram which shows the line runs from the road, down my driveway, along the side of the house before turning across the rear. See the dodgy MS Paint diagram below.
I was told by the SGN engineer that I was not to disturb the pipe under any circumstances, so digging under it to run the armoured isn't an option. The property is a bungalow, so running a cable across on a catenary isn't viable either.
I'd like to know what would be a reasonable approach to getting a cable run in a compliant manner - any help or advice appreciated.