Insulation test L to E long length of SWA | on ElectriciansForums

Discuss Insulation test L to E long length of SWA in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Joined
Feb 7, 2009
Messages
360
Reaction score
16
Location
.
Insulation test live to earth = 0.7 ohms.
This is a long length of buried swa cable (approx 100m) from mains in to submain.
Test done with live and earth disconected at main and with switch off at sub main.
Question - is this an accurate reading or am I misding something.
Its a big job to replace if I've got this wrong ?
 

Attachments

  • [ElectriciansForums.net] Insulation test L to E long length of SWA
    20240228_091021.jpg
    565.6 KB · Views: 25
If this is a genuine reading, then the cable is severely damaged, and must be repaired, replaced, or taken out of service.
Why would L+N to earth give any better reading?
Chances are that the cable is damaged at one point, and similar measurements taken at the other end of the cable should give some indication of where.
 
Also the CPC should be connected to earth during any IR tests.

Here (if SWA) it is very unlikely to make a difference, but more generally with stuff like T&E you can have a live nicked by a screw/nail and it is leaking to the wall, etc, but not to the CPC that still has the insulation separating them (and from wall, etc).
 
So is it 0.70 ohms or 0.70 Mohm?
very good question and I was just about to aske the exact same question, hopefully the OP will come back and answer it
 
Also the CPC should be connected to earth during any IR tests.

Here (if SWA) it is very unlikely to make a difference, but more generally with stuff like T&E you can have a live nicked by a screw/nail and it is leaking to the wall, etc, but not to the CPC that still has the insulation separating them (and from wall, etc).
2 core swa and armour used as earth
 
Is that with whatever's at the far end switched off?
No tripping when sub main switched off as that was only briefly while testing .
Live and earth disconnected at front end (neutral still connected) and mains switch and all breakers off at back end to test. Random tripping was when all on (2 to 3 times in last 24 hrs)
 
I should also say that this swa cable has a 63a mcb at the front end and is randomly tripping ?
If it randomly trips with the load-end of the SWA isolated then it confirm the IR results that the cable is damaged somewhere.

Most likely you see your 0.7 M ohm result after it has gone "Bang!" internally and you go to test it, then after time water creeps back in and it goes bang once more, etc.

There are techniques to help locate where along the cable a fault it, but some depend on it being a low and stable short (so you can see the relative resistance to a fault from the cable ends to guess approximately the ratio of cable to it), and others require expensive time-domain reflection sort of equipment (to look at the waves bouncing around just after it clears a fault). Has there been any civil works, digging of gardens, etc, recently? That might point to a likely location.

But it could just be poorly installed cable without sand/fine gravel around the cable resulting in a stone crushing it over time.
 
Underground and laid about 20 plus years ago.
You say it is about 100m long, walk the route if you know it and look for possible disturbances, like cultivated ground, new fence posts etc. A common method of localising is to dig down half way and cut and test the cable. Then repeat until the fault is located. But be careful to make sure that you cut the correct cable. You have to risk assess, are there other cables in the area? Can they be isolated while you cut? It just a matter of patience and thinking. I know some people on here don't like the idea of joints, but done correctly they should be as good as the cable. I come from a DNO background and have used this method many times.
 
There are techniques to help locate where along the cable a fault it, but some depend on it being a low and stable short (so you can see the relative resistance to a fault from the cable ends to guess approximately the ratio of cable to it), and others require expensive time-domain reflection sort of equipment (to look at the waves bouncing around just after it clears a fault). Has there been any civil works, digging of gardens, etc, recently? That might point to a likely location.
^^ This is the bottom line.
Have a good look for any recent activity.
If that fails, you might find an older sparks locally that still has a wind up megger that does Varley loop tests, or someone that has a Megger Bridge, or an even older person who has a Post Office box! This all requires
1) you know the route
2) there is one undamaged core
3) the fault to earth has a stable resistance (as @pc1966 said)

If that fails you are into hiring a TDR- again you need to know the route for this to help, and therefore extra cable tracing tools to determine the path might be needed.

On jobs like this that I've done it tends to end up either
-easily finding the reason (shiny new fence post) or
-identifying roughly which section of the cable is faulty without finding the reason, making cuts, establishing the remainder is fine, and running a new section.
 

Reply to Insulation test L to E long length of SWA in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
162
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
Replies
21
Views
987
nicebutdim
N
When working in the motor repairs industry you have to fill in test sheets and keep them for so long. Doing that will do is ok for most things but...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks