Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the weekend.
I was called to attend a domestic property where the tenant had mentioned getting a shock when touching a tiled wall and the bath taps.
On arrival and inspection I was in fact getting varied readings around 24v when using my voltage indicators between the two.
When isolating the first floor socket circuit the fault appears to clear and I can no longer measure voltage. On further inspection there is a spurred single socket on the other side of the wall, this is fed from a blanked point which I assume was part of the ring final, also on the same all but approx 4ft away inside a cupboard. Disconnecting the spurred leg to the single socket and energising the circuit again also seems to clear the fault.
The tiling has clearly suffered damage in areas with some tiles being replaced really badly, so my initial thoughts were somehow that spurred leg has got damaged and water ingress has soaked that wall causing the issue. Voltage is measured specifically around the areas of damaged tiles and not higher up the wall.
My concerns lie with the the fact that this circuit is protected by a 32a Type A RCBO, which has not tripped. This is a TT earthing arrangement and I have measured 47.5ohms, visually the clamp looked ok. Bonding was seen to gas and water services in the garage correctly located but I hadn’t verified via a wander lead.
The RCBO appears to test out fine on 1x/5x tests and also ramp tests.
Prior to disconnecting the spurred point I measured really low IR readings across L to E and N to E. Again when disconnecting the spurred leg, the IR improves to 120Mohms plus.
For good measure I tested the spurred leg that is on the wall the other side of the bath when completely disconnected and I get 999Mohms. So this confused me even more if I’m honest.
Some outside opinion would be great to see if I am missing something blatantly obvious here. Could there be some plastic paperwork preventing adequate bonding of pipe work to taps? Why has the RCBO not taken out the supply to this circuit etc.
Thanks in advance and apologise for the long essay.
Regards
I was called to attend a domestic property where the tenant had mentioned getting a shock when touching a tiled wall and the bath taps.
On arrival and inspection I was in fact getting varied readings around 24v when using my voltage indicators between the two.
When isolating the first floor socket circuit the fault appears to clear and I can no longer measure voltage. On further inspection there is a spurred single socket on the other side of the wall, this is fed from a blanked point which I assume was part of the ring final, also on the same all but approx 4ft away inside a cupboard. Disconnecting the spurred leg to the single socket and energising the circuit again also seems to clear the fault.
The tiling has clearly suffered damage in areas with some tiles being replaced really badly, so my initial thoughts were somehow that spurred leg has got damaged and water ingress has soaked that wall causing the issue. Voltage is measured specifically around the areas of damaged tiles and not higher up the wall.
My concerns lie with the the fact that this circuit is protected by a 32a Type A RCBO, which has not tripped. This is a TT earthing arrangement and I have measured 47.5ohms, visually the clamp looked ok. Bonding was seen to gas and water services in the garage correctly located but I hadn’t verified via a wander lead.
The RCBO appears to test out fine on 1x/5x tests and also ramp tests.
Prior to disconnecting the spurred point I measured really low IR readings across L to E and N to E. Again when disconnecting the spurred leg, the IR improves to 120Mohms plus.
For good measure I tested the spurred leg that is on the wall the other side of the bath when completely disconnected and I get 999Mohms. So this confused me even more if I’m honest.
Some outside opinion would be great to see if I am missing something blatantly obvious here. Could there be some plastic paperwork preventing adequate bonding of pipe work to taps? Why has the RCBO not taken out the supply to this circuit etc.
Thanks in advance and apologise for the long essay.
Regards