Is blue neutral or earth when there is a black cable (which is the old neutral) - old system? Other one is red, no green / yellow
[ElectriciansForums.net] Red, blue and black cable
In some older buildings where there was 3 phase supplies serving single phase loads, and the installation was singles in conduit…. The phase colours were used.
So normally where you would see red, black and g/y, you could have yellow, black, g/y or blue, black, g/y
If metal conduit, there may be no green/yellow…
What is the situation you have found?
BTW, @buzzlightyear why is your diagram showing the cores in the wrong order? Old 3 core and earth is red, yellow, blue…. And your new cables on the right are similarly mixed up…. Should be brown, black, grey.
I’m not 100% certain the cpcs are in the right place either.
6 Changes to cable core colour identification​
Table 7B – Cable to BS 6004 (flat cable with bare cpc)​
Cable typeOld core coloursNew core colours
Single-core + bare cpcRed or blackBrown or blue
Two-core + bare cpcRed, blackBrown, blue
Alt. Two-core + bare cpcRed, redBrown, brown
Three-core + bare cpcRed, yellow, blueBrown, black, grey
Some of the vauxhall factory in Luton is wired like this the live is the colour of what phase it goes to in the DB
Reply to Red, blue and black cable in the UK Electrical Forum area at ElectriciansForums.net
Time to get an electrician.
Yes still see the odd red white and blue out in the wild, usually without cpc, iirc that colour code was only used for a short time...could be...