Hi All,

My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our equipment that each have a Surge Protected Extension Lead mounted into them, they're Class I, and we test them on 250V. Earth Cont. and IEC Cont. are both fine, but Insulation Resistance is reading below the minimum 1Mohm that a Class I appliance should have, they're reading 0.52Mohm.

We're unsure whether they Pass or Fail as we know that Surge Protected leads would fail a typical test, and we've tested them at lower voltage, but we don't know what to do with them.

If anyone could lend any insight to what they would do, would be greatly appreciated.
 
TL;DR
Surge Protected Extension Leads failing IR PAT Test, unsure what to do as I know Surge Prot is typically meant to fail a normal test.

Attachments

  • [ElectriciansForums.net] PAT FAIL HELP - 19" Rack Mounted Surge Protected Power Strip
    20240417_160110.jpg
    326.3 KB · Views: 20
  • [ElectriciansForums.net] PAT FAIL HELP - 19" Rack Mounted Surge Protected Power Strip
    20240417_160101.jpg
    252.1 KB · Views: 20
  • [ElectriciansForums.net] PAT FAIL HELP - 19" Rack Mounted Surge Protected Power Strip
    20240417_160057.jpg
    317.6 KB · Views: 20
SPD would usually pass at 250v dc but not at 500 v ,it could be the spd itself . i would contact the manufacturer for advice and expected readings
They were bought off Amazon, unsure what manufacturer;

We've also had a couple that have tested above the 1Mohm mark, and we've spoken with our GM and we'll see how many total have failed as to what we do moving forwards - we have agreed to take them out of use and may replace them or look at other options
 
There is an other issue wit useing 19" racks on 13A plugs, the earth leakage of all the kit addeds up. If you have an earth condutor break then all that kit becomes live and give someone a nasty shock. Put the surge protection at the distribution board, use some decent ABB or similar surge kit. As for the sockets have a look at Olson and consider a 16A commando socket.
 
Put the surge protection at the distribution board, use some decent ABB or similar surge kit.

You have no control over what is installed in the buildings the racks get taken to so whatever protection is required needs to be in the rack.

As for the sockets have a look at Olson and consider a 16A commando socket.

That's ok as long as every where you take it has 16A outlets, otherwise it will just be plugged in via a 13-16 adaptor.
 
You have no control over what is installed in the buildings the racks get taken to so whatever protection is required needs to be in the rack.



That's ok as long as every where you take it has 16A outlets, otherwise it will just be plugged in via a 13-16 adaptor.
Have a look at electrical.------.org/wiring-matters/years/2022/93-november-2022/high-protective-conductor-currents-in-electrical-installations/ the current in the protective conductor could be 3.5mA for each class 1 appliance.
I stand by my comment about surge protection, cheap surge protection is a fire hazard.

replace the ---- with the iet no space
 
Have a look at electrical.------.org/wiring-matters/years/2022/93-november-2022/high-protective-conductor-currents-in-electrical-installations/ the current in the protective conductor could be 3.5mA for each class 1 appliance.
I stand by my comment about surge protection, cheap surge protection is a fire hazard.

replace the ---- with the iet no space

Yes, but unless you are permanently installing the rack somewhere you have little control over what supply is going to be available or how it is protected.

Yes cheap surge protection could be dangerous, but that doesn't mean surge protection can't be installed in a rack, just that it should be of a good quality.
 
There is an other issue wit useing 19" racks on 13A plugs, the earth leakage of all the kit addeds up. If you have an earth condutor break then all that kit becomes live and give someone a nasty shock. Put the surge protection at the distribution board, use some decent ABB or similar surge kit. As for the sockets have a look at Olson and consider a 16A commando socket.
How would using a commando instead of a 13amp plug make any difference when there's a loss of the cpc, You're still going to have the same accumulated earth leakage.
 
Last edited:

Reply to PAT FAIL HELP - 19" Rack Mounted Surge Protected Power Strip in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

Heh I know the brochures for courses with stock images of women using tools in random scenarios but when you're there it never happens, it's all...
    • Like
Replies
2
Views
357

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top