Need help about Surge Protective Device | on ElectriciansForums

Discuss Need help about Surge Protective Device in the UK Electrical Forum area at ElectriciansForums.net

Joined
Apr 28, 2024
Messages
3
Reaction score
0
Location
West Bengal. India
Recently I have installed Type 2 Surge Protective Device SPD 20 to 40kA, Type1+2, Phase + Neutral + Earth (2 Pole 275 Volt AC) (Uc-275VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV) after 64A DP MCB at home MDB. The home lode is around 1.75KW. We have 220 VAC main line here.

At the evening of 3rd day after installation, the SPD was exploded. I find that the cartridge of Phase side was damaged and it was totally short with earthing terminal. But cartridge of neutral side was in good condition. There was no sign of lightning nearby. No neighbour was affected with Spikes and surges at that time. I am confused about the reason how the SPD got damaged!

Now I am going to replace the SPD with “Type 2 Surge Protective Device SPD (Phase side: Uc-320VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV Neutral Side: Uc-255VAC, In-20KA, Imax-40KA, Up ≤ 1.5 KV). Will it be good?

Thanks.
 
A starting point is what make/model of SPD did you fit? A photo might help here.

Normally SPD have internal thermal fuses to deal with overheating, and for worst-case protection they depend on either the incoming supply's over-current protection, or for smaller SPD they depend on a MCB just for the SPD.

SPD are designed to deal with very short-term surges, so tens of microseconds from induced lightning current or the switching of large motors, etc. Where they are at serious risk of overheating is when you have a long-duration over-voltage situation, for example, a power cross situation (when a HV cable falls and strikes a LV cable) or an open neutral in an unbalanced 3-phase system, etc.

However, any reputable SPD should fail safe in such conditions with the internal thermal fuse (basically solder joint) opening to disconnect before it reaches a dangerous temperature.

What will case even a good SPD to fail catastrophically is a short surge beyond its energy handling limits, but that is unusual outside of a direct lightning strike the the building, or to a strike to an overhead power line within a km or so of the SPD. You are down as from India, that has more thunderstorm days than the UK where I am by an order of magnitude but I guess it varies dramatically over your country.
 
Last edited:
A starting point is what make/model of SPD did you fit? A photo might help here.

Normally SPD have internal thermal fuses to deal with overheating, and for worst-case protection they depend on either the incoming supply's over-current protection, or for smaller SPD they depend on a MCB just for the SPD.

SPD are designed to deal with very short-term surges, so tens of microseconds from induced lightning current or the switching of large motors, etc. Where they are at serious risk of overheating is when you have a long-duration over-voltage situation, for example, a power cross situation (when a HV cable falls and strikes a LV cable) or an open neutral in an unbalanced 3-phase system, etc.

However, any reputable SPD should fail safe in such conditions with the internal thermal fuse (basically solder joint) opening to disconnect before it reaches a dangerous temperature.

What will case even a good SPD to fail catastrophically is a short surge beyond its energy handling limits, but that is unusual outside of a direct lightning strike the the building, or to a strike to an overhead power line within a km or so of the SPD. You are down as from India, that has more thunderstorm days than the UK where I am by an order of magnitude but I guess it varies dramatically over your country.
 

Attachments

  • [ElectriciansForums.net] Need help about Surge Protective Device
    Euro.jpg
    49 KB · Views: 32
This might also be worth considering:
What is your opinion about this
 
What is your opinion about this
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct strike.

Type 2 SPD are for induced surges, i.e. nearby strike, whereas Type 1 or Type 1+2 are able to cope with higher energy surges from a hit to the building's lightning protection system, or to an overhead cable some distance away.
 

Reply to Need help about Surge Protective Device in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top