Hi All,
I have these old light switches.
I understand this yellow / blue is the old pre 1980 colour scheme.
Is it correct that:
1. YELLOW with a red sleeve is LIVE
2. BLUE with a red sleeve is NEUTRAL
?
Thanks
 

Attachments

  • [ElectriciansForums.net] Old light switches wiring
    1.jpeg
    217.5 KB · Views: 108
  • [ElectriciansForums.net] Old light switches wiring
    2.jpeg
    159.7 KB · Views: 78
No Neutral involved. Any cables with red sleeving should be switched lives, in this case 'strappers' for a 2way light.
Why do you ask? Are you changing the switches?
That back box lug on the 1 gang doesn't seem to be in the best of health.
 
No Neutral involved. Any cables with red sleeving should be switched lives, in this case 'strappers' for a 2way light.
Why do you ask? Are you changing the switches?
That back box lug on the 1 gang doesn't seem to be in the best of health.
The electronic switch I am adding has "L In" and "L Out" and yes this switch does not require Neutral. "L Out" leads to the bulb.

Yeah the box lug looks loose, it's in a plasterboard wall with a void.
 
First switch I presume is a 1 way and a 2 way…
Second switch is the paired 2 way.

Looking at the wiring, you may have a permanent live at both boxes, which could be 2 separate circuits.

Isolate before messing around.

Try to fix the screw lug, or replace the box entirely. Looks broken, not just loose.

If you have an electronic switch… which make? As they can work different ways.

Are you replacing both switches, or just one that controls both lights?

And finally… those are shallow boxes. Will you get an electronic switch to fit? You may need a plastic extension spacer to bring it out from the wall a bit.
 
The electronic switch I am adding has "L In" and "L Out" and yes this switch does not require Neutral. "L Out" leads to the bulb.

Yeah the box lug looks loose, it's in a plasterboard wall with a void.
Just get a pro in to sort it, Malcolm.

I see you're in London, though. A couple of hours' all in......£400ish???

Oh, Plus a tenner for mats.;)
 
Last edited:
First switch I presume is a 1 way and a 2 way…
Second switch is the paired 2 way.

Looking at the wiring, you may have a permanent live at both boxes, which could be 2 separate circuits.

Isolate before messing around.

Try to fix the screw lug, or replace the box entirely. Looks broken, not just loose.

If you have an electronic switch… which make? As they can work different ways.

Are you replacing both switches, or just one that controls both lights?

And finally… those are shallow boxes. Will you get an electronic switch to fit? You may need a plastic extension spacer to bring it out from the wall a bit.
Yes, you are right, two separate circuits (upstairs, downstairs lights) but in 2-way configuration across 2 circuits.
Yes, I am going to fix the box lug
Yes, well spotted I will need the extension spacer for the shallow one.
Yes, same electronic switch per box
This is the diagram of the electronic switch.
[ElectriciansForums.net] Old light switches wiring
 
Last edited by a moderator:
Malcolm - I'm not sure what your question is!

Use the top left wiring diagram for putting one Sonos with the single switch, establish which of those two wires is permanent (L), wire then accordingly to the Sonos L terminals, and then wire the switch directly to S1 & S2.

Use the top right diagram to wire the 2-way switch, reconfiguring the 3 core cable to mimic that diagram. Put the other Sonos with this switch. Establish which of the two non-3 core conductors is permanent (L) as before, and wire that to the Sonos Lin as before, the other wire to Lout. Then wire the 3-core to match the circuit diagram for the S1 & S2 connections.

If you don't have test equipment, or are uncertain about implementing the diagrams, you may need some help.
 
I have checked all the wires with a multimeter and the ones marked in violet colour are permanent lives. Permanent lives in each box are red and indistinguishable from the other red ones.

# 1-WAY SWITCH (upstairs)
COM - yellow (with red sleeve)
WAY L1 - blue (with red sleeve) + red -> permanent live
WAY L2 - 2x red

#2-WAT SWITCH (downstairs)
BOTTOM
COM - yellow (with red sleeve)
WAY L1 - red -> permanent live

TOP
WAY L1 - blue (with red sleeve)
WAY L2 - red
COM - red

From what I red online COM supposed to be LIVE (PERMANENT) and L1 should be SWITCHED LIVE but in this case permanent goes to L1 in both boxes.
Does it makes sense to you or is it mixed up?
 

Attachments

  • [ElectriciansForums.net] Old light switches wiring
    31.jpeg
    240.2 KB · Views: 45
  • [ElectriciansForums.net] Old light switches wiring
    11.jpeg
    322.8 KB · Views: 35
We can see what is going on from your photos. You obviously don't understand the 2-way wiring method involved.
Don't take as red all you reed online.
As above (and previously) professional help is advised.
 
You misunderstand the terminals of the switches, or if you don't, you chose a bizarre way of representing the information in your table of results. Each switch has terminals in a triangle, as I've tried to show in the second pic below.

So unravelling your list, you have traditionally wired circuits, nothing is mixed up.
It's like this for the two-way circuit:

[ElectriciansForums.net] Old light switches wiring

It needs to be wired as I suggested previously.
In order to implement the 2-way Sonos circuit, the upstairs wiring to the switch will have to be changed.
If you are not sure how to do this, do get some help, as there is plenty of opportunity to blow up the Sonos device, have an accident, or leave something dangerous behind.

[ElectriciansForums.net] Old light switches wiring
 
Last edited:
From what I red online COM supposed to be LIVE (PERMANENT) and L1 should be SWITCHED LIVE but in this case permanent goes to L1 in both boxes.

From what I've read online the earth is flat and run by giant lizard people who live underground.

Don't believe what you read online.

There is no 'supposed to be' as far as the terminals on those switches are concerned. Com, L1 and L2 are just three terminals on a switch which will be connected differently depending on how they are being used, for extra fun different manufacturers sometimes label them differently.

Does it makes sense to you or is it mixed up?

Makes perfect sense to me.
 
Hi again Everyone,
You were helpful to me especially Avo Mk8 is very understanding. I made this diagram.
Perhaps you will say it's wrong :)

So far I connected the switch downstairs, it works, I left the blue and yellow wires aside for now but for some reason I lost the current upstairs, not sure why. It's on a separate circuit, the RCB is ON but no lights upstairs.
 

Attachments

  • [ElectriciansForums.net] Old light switches wiring
    2waysocket.jpg
    54.1 KB · Views: 31
So far I connected the switch downstairs, it works, I left the blue and yellow wires aside for now but for some reason I lost the current upstairs, not sure why. It's on a separate circuit, the RCB is ON but no lights upstairs.
Your diagram is of how the old switches are/were wired, and as far as I can see, is correct.
It does not represent how to connect the Sonos.

With the yellow and blue wires disconnected, the light will never come on because you have removed the way the bulb gets power.

The Sonos needs to be connected as per the top right diagram in your post #6.

This forum is not supposed to give step by step instructions for obvious reasons.
I'm feeling that since you are already involved in this, somewhat against the advice already given, I will give a factual explanation of the necessary wiring. It needs to be carried out safely and competently, which you need to organise.

The red wire to the upstairs light bulb should be in Sonos L out, and the incoming power (circuit 2) red wire should be in Sonos L in.

The end of the yellow wire that used to be in upstairs switch com (that you say is presently unconnected) should be in Sonos S2.

The blue wire (that you say is presently unconnected) should go to the upstairs switch L1 where it was originally.

A short piece of insulated wire is needed between the upstairs switch Com and Sonos S1.

The end result should be that there is only one wire in each old 2-way switch terminal, and only one wire in each Sonos terminal.
 
Ok, thanks again.
I meant the lights not only in the hallway but across the whole 1st floor are gone.
RCB says "lights+smoke detector". When that RCB is on I can see the green light on the smoke detector but other than that no power to any of the lights. When off the green light on the detector goes off as well. The red wire in upstairs light socket that use to have current is dead now. Did I blow some fuse or the RCB malfunctions?
 
Ok, thanks again.
I meant the lights not only in the hallway but across the whole 1st floor are gone.
RCB says "lights+smoke detector". When that RCB is on I can see the green light on the smoke detector but other than that no power to any of the lights. When off the green light on the detector goes off as well. The red wire in upstairs light socket that use to have current is dead now. Did I blow some fuse or the RCB malfunctions?
Oh, I see, I hadn't understood that, sorry.
Difficult to diagnose remotely.
Is the individual Breaker that tripped, an MCB, RCBO or an RCD. Unusual to be the latter for an individual circuit?
If switching the 'RCB' causes the smoke detector light to be on/off, sounds as if the breaker is providing power when on.
Is there some other protective device on your lighting circuit? Nothing else tripped?

Have you put the wires back in the upstairs switch exactly as they used to be, and if so does that restore power? There might be a link to those cables somewhere we don't know about?
 
Last edited:
Oh, I see, I hadn't understood that, sorry.
Difficult to diagnose remotely.
Is the individual Breaker that tripped, an MCB, RCBO or an RCD. Unusual to be the latter for an individual circuit?
If switching the 'RCB' causes the smoke detector light to be on/off, sounds as if the breaker is providing power when on.
Is there some other protective device on your lighting circuit? Nothing else tripped?

Have you put the wires back in the upstairs switch exactly as they used to be, and if so does that restore power? There might be a link to those cables somewhere we don't know about?
As far as I can see nothing has tripped in the consumer unit. There is a separate fused switch next to the consumer unit (it says smoke detector) I reckon it's the downstairs one? This rather old consumer unit is going to be replaced at some point this year.

Do you mean I broke the series? I am going to check all the wires for current.
 

Attachments

  • [ElectriciansForums.net] Old light switches wiring
    consumerunit2.jpg
    216.2 KB · Views: 22
  • [ElectriciansForums.net] Old light switches wiring
    consumerunit3.jpg
    194.7 KB · Views: 24
I checked all the exposed wires upstairs and none of them are live.

I admit at the time I was messing around with a ceiling rose in the bathroom but this one is only 3 wire (green-yellow one grounding the ceiling rose and two red ones that are not live)

The fused switch next to the consumer unit is for both smoke detectors upstairs and downstairs one, so when this one is OFF both smoke detectors go OFF.
 
Is the MCB on the very right labelled "Lights & smoke alarms" the one you turned off when you said turning it off made the green light on the alarm go off?
Have you turned that MCB off and on again since the fault. Very rarely a MCB can trip without its lever going down. Just checking!
I'm afraid I have no idea why power should no longer be present for upstairs lights, unless you have disturbed something, possibly unknowingly, somewhere!
 
I admit at the time I was messing around with a ceiling rose in the bathroom but this one is only 3 wire (green-yellow one grounding the ceiling rose and two red ones that are not live)
It's unusual not to have a black neutral wire at a ceiling rose, or rather, unusual to have the neutral as red. Are you sure there aren't any other wires that might have escaped from that ceiling rose?
 
Is the MCB on the very right labelled "Lights & smoke alarms" the one you turned off when you said turning it off made the green light on the alarm go off?
Have you turned that MCB off and on again since the fault. Very rarely a MCB can trip without its lever going down. Just checking!
I'm afraid I have no idea why power should no longer be present for upstairs lights, unless you have disturbed something, possibly unknowingly, somewhere!
Correct, it's that MCB that disconnects power to upstairs lights and that smoke detector upstairs.
The fused switch (not on the pictures) but next to consumer unit when OFF switches both upstairs and downstairs smoke detectors OFF.
I did switch this MCB several times and to OFF position not to work on live wires.
 
It's unusual not to have a black neutral wire at a ceiling rose, or rather, unusual to have the neutral as red. Are you sure there aren't any other wires that might have escaped from that ceiling rose?
I said it wrong. It's not a ceiling rose in the bathroom but just a pull cord switch but I was wondering if there is anything in one of those ceiling roses that can trip. I haven't been touching them. I reckon to access roses I need to go to the loft.
 
I said it wrong. It's not a ceiling rose in the bathroom but just a pull cord switch but I was wondering if there is anything in one of those ceiling roses that can trip. I haven't been touching them. I reckon to access roses I need to go to the loft.

If the tripping is a new development, it's more than likely going to be related to recent tinkering.
 
I checked all the exposed wires upstairs and none of them are live.

I admit at the time I was messing around with a ceiling rose in the bathroom but this one is only 3 wire (green-yellow one grounding the ceiling rose and two red ones that are not live)
Sorry to say it but this sums things up nicely.
 

Reply to Old light switches wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Yes still see the odd red white and blue out in the wild, usually without cpc, iirc that colour code was only used for a short time...could be...
Replies
13
Views
820
Furthermore, as the left hand switch will currently not do anything, I'd try the loose brown in here:
Replies
4
Views
303
  • Question
Ah yes my apologies, thank you much appreciated.
Replies
5
Views
749
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
1K
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top