BG are stating that these are 18th edition compliant. I'm doubtful if they meet regulations 536.4.3.2 & 536.4.202 - overload protection of switches and RCCBs.
the RCDs are rated at 63A. There is no way of configuring the supplied MCBs that doesn't exceed 63A.
I guess if the main fuse was 60A it might be compliant but then would there not be an issue with the potential load of the installation being > 60A causing the DNO fuse to blow?
- TL;DR
- BG claim split load board with 63A RCDs is 18th compliant