2 x t&e for 3 phase isolator | on ElectriciansForums

Discuss 2 x t&e for 3 phase isolator in the UK Electrical Forum area at ElectriciansForums.net

kev.k

-
Joined
Jan 18, 2015
Messages
26
Reaction score
11
Location
Manchester
Hi All!

Came across this yesterday and just wanted to get others opinion. 3 phase isolator wired in 6mm twin and earth x 2, i'm guessing it's not against regs? Obviously not the best way to do it but would anybody pull this on EICR? It's wired in 25mm pvc conduit on 32a breaker, assume they couldn't be bothered going wholesalers for some 5 core SWA.

Thanks
[ElectriciansForums.net] 2 x t&e for 3 phase isolator
[ElectriciansForums.net] 2 x t&e for 3 phase isolator
 
It’s a C3. Somewhere in the regs (I would have to have a copy with me to remind myself where!) there is commentary that all line conductors have to be within the same overall sheath/mech protection. The reason being is that by having effectively 2x together and 1x separate they will have heat dissipation at different rates, therefore different resistances.

Apart from being dog rough.
 
Hey! Yeah, it’s not ideal, but I don’t think it’s breaking any regs either. The twin and earth in conduit should be fine for the 32A breaker. Wouldn't pull it on an EICR myself.

Technically it does as Westward eluded to "Definitely needs a note see Regulation 521.8.1." Also this has come up here a few years ago and the same Reg was mentioned then. I don't have the book to hand to check it but would trust it is correct.
 
Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back.
Effectively carried out a 'FI (Further Investigation)' at the time to establish what had been done as not immediately obvious. - 3 identical heaters so balanced load, 1core of 1 t&e acting as neutral for the 3ph, and ccc large enough should only 2 heaters be used at any one time. Unable to establish cable routes but R1+R2 test concurred cables to be of identical length.
Nothing immediately dangerous although not compliant so declared C3.

As for original post, if all within conduit then no code! but labelled per #2
 

Reply to 2 x t&e for 3 phase isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
288
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top