How is the direction of this motor controlled Gauge door opened ( 240v AC) | on ElectriciansForums

Discuss How is the direction of this motor controlled Gauge door opened ( 240v AC) in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 6, 2024
Messages
1
Reaction score
0
Location
Uk
How is the direction this motor spins controles from what I can trace the white is directly attached to the neutral. ( Might be wrong on that, ) Thanks in advance, Simon
[ElectriciansForums.net] How is the direction of this motor controlled Gauge door opened ( 240v AC)
[ElectriciansForums.net] How is the direction of this motor controlled Gauge door opened ( 240v AC)
 
You are correct that the white wire should connect to Neutral.
Then the capacitor connects between red and blue (capacitor with twin tags on each terminal for convenience of wiring)
You apply power (eg Live) to the red capacitor tag to make it go one way, or apply it to the blue tag to go the other.

To implement that you could use a momentary (sprung) single pole two way (spdt) switch, with the Live feed connected to the switch centre/common terminal.

The motor is rated for intermittent use, so you wouldn't want to run it for many minutes continuously otherwise its thermal protection might kick in and the motor stop.

NB: Reference to Live and Neutral assumes you are using a 120V supply! (Motor states 120V 60Hz which is not UK mains)
 

Reply to How is the direction of this motor controlled Gauge door opened ( 240v AC) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
370
Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Replies
1
Views
176

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top