EICR Findings - Advice on Coding Required | on ElectriciansForums

Discuss EICR Findings - Advice on Coding Required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Sep 30, 2022
Messages
24
Reaction score
2
Location
London
Hi everyone,

I recently completed a domestic EICR and came across something unusual. There’s a 10mm² twin and earth cable directly connected to the 100A cut-out fuse at the service head. The cable is concealed within the client’s wall and reappears next to the consumer unit, where it connects to a feeding cable that supplies the neighboring property.

After further investigation, I discovered that this cable is supplying power to the off-license shop next door and two flats above it.

Would you classify this as a C2? I’d appreciate your thoughts on this situation.

[ElectriciansForums.net] EICR Findings - Advice on Coding Required

[ElectriciansForums.net] EICR Findings - Advice on Coding Required

[ElectriciansForums.net] EICR Findings - Advice on Coding Required

[ElectriciansForums.net] EICR Findings - Advice on Coding Required
 
Hi everyone,

I recently completed a domestic EICR and came across something unusual. There’s a 10mm² twin and earth cable directly connected to the 100A cut-out fuse at the service head. The cable is concealed within the client’s wall and reappears next to the consumer unit, where it connects to a feeding cable that supplies the neighboring property.

After further investigation, I discovered that this cable is supplying power to the off-license shop next door and two flats above it.

Would you classify this as a C2? I’d appreciate your thoughts on this situation.

View attachment 118398

View attachment 118399

View attachment 118400

View attachment 118401
You need to contact the client and inform him that it needs to be disconnected.
If you leave it connected, then you are complicit in theft of electricity.
 
No seals on the main fuses kinda says it all…. Along with the total lack of green/yellow sleeving.

But impressive for that size of cable to be feeding an off license, 2 flats, and I wouldn’t be surprised, at a herb garden in the attic
 
Is this a joke?

Incredibly wrong if this is real. Sod the EICR and just condemn it
It's real. I failed tge EICR, but someone from UKPNetworks came, and said that this is not a subject to my report, as it is feeding the next door. I think because the connection is in the living room and the cable passes through the property, it is a subject of my report. Your opinion?
 
Both right.

It is before any meter, so not part of the fixed wiring that you are testing. Not a final circuit… BUT there is a box on an EICR for “condition of incoming equipment” or whatever… which you can still code.

C1 it on whatever you can. It needs fixed, but I doubt it will be done.
 
Both right.

It is before any meter, so not part of the fixed wiring that you are testing. Not a final circuit… BUT there is a box on an EICR for “condition of incoming equipment” or whatever… which you can still code.

C1 it on whatever you can. It needs fixed, but I doubt it will be done.
I took of the covers of the junction boxes. Is it C2 with the covers, or not part of the fixed wiring installation?
 
You need to contact the client and inform him that it needs to be disconnected.
If you leave it connected, then you are complicit in theft of electricity.
The client is informed, and they informed the UKPNetwork. The from the network said, that it is not part of the installation and I should not code it at all. But the cable passes through the property I am inspecting, and if it overheats, the client is in danger. Am I right?
 
The client is informed, and they informed the UKPNetwork. The from the network said, that it is not part of the installation and I should not code it at all. But the cable passes through the property I am inspecting, and if it overheats, the client is in danger. Am I right?
I would get the dno to come and look at it.
 
I was just saying C1 so it might push someone to get it sorted.

The round joint box is only rated to 30A…. The 10mm I would think is undersized… depending what size is in the actual fuse.

Just mention it on your report, get paid, then it’s up to the customer.
 
I was just saying C1 so it might push someone to get it sorted.

The round joint box is only rated to 30A…. The 10mm I would think is undersized… depending what size is in the actual fuse.

Just mention it on your report, get paid, then it’s up to the customer.
That is what i am going to do. Thanks mate!
 

Reply to EICR Findings - Advice on Coding Required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top