So, I'm stuck.

There is a metal light switch, which has a noticeable vibration to it when you touch. Like a humming on your finger.

It is a 2 way at the bottom of the stairs. The 50V is only present when the lights are switched on. I tried changing the switch, no effect.

I haven't a clue! What it could be.

20250114_123801.jpg


20250114_123340.jpg


20250114_123226.jpg


20250114_123232.jpg


20250114_122527.jpg
 
There are a couple of things that could be wrong.
It may be that you are measuring an induced voltage on an otherwise dead leg of the strappers .
It could be a faulty switch with a large voltage drop across the contacts.
 
It may be that you are measuring an induced voltage on an otherwise dead leg of the strappers .
James makes an important point here. Did you measure the voltage on the blue wire as well as the yellow? If the blue is the strapper in use, and measures 230V, then a random induced voltage on the yellow, when measured with a high impedance meter, would be normal and expected.
 
James makes an important point here. Did you measure the voltage on the blue wire as well as the yellow? If the blue is the strapper in use, and measures 230V, then a random induced voltage on the yellow, when measured with a high impedance meter, would be normal and expected.
I will do this 🫡

But, any idea why my volt meter, flashes showing AC volts (no measurement) when I put it on the metal face plate?
 

Reply to 50v on CPC on front plate. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
749
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

I was considering that, however the loft isn't boarded, not exactly the lightest 🤣 I was hoping I wouldn't have to do that but maybe that's the...
Replies
2
Views
205
Depending on the location of the 2 CU's and the quality of materials I'd say ÂŁ10K-12K. If they're potential tyre kickers don't waste loads of time...
    • Informative
Replies
4
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top