NO CPC's

EddieB

-
Arms
just helped a mate move into his house, new consumer unit fitted with RCBO's etc test sheet supplied, but no cpc's at the switches
 
and?

No cpc in historic lighting cable is permissible, certain conditions have to be met to sign it off as safe though.

Is the place rented?
 
The boxes may be metal, but is there an insulated block for the faceplate screws to go into? Thus electrically separating the screws from the box itself.

Another thing they used to do was use plastic screws….

And of course, only class II switches and light fittings. No fancy decorative metal plates.



I think nowadays, the consensus is to recommend a rewire when no cpc present…. And sometimes, it’s not actually difficult if the wiring is in conduit.

Speaking of which, a lot of “new” testers don’t cotton on to the fact that continuous steel conduit IS the cpc. If they don’t see a green and yellow wire, they mark it down as no cpc.
 
The boxes may be metal, but is there an insulated block for the faceplate screws to go into? Thus electrically separating the screws from the box itself.

Another thing they used to do was use plastic screws….

And of course, only class II switches and light fittings. No fancy decorative metal plates.



I think nowadays, the consensus is to recommend a rewire when no cpc present…. And sometimes, it’s not actually difficult if the wiring is in conduit.

Speaking of which, a lot of “new” testers don’t cotton on to the fact that continuous steel conduit IS the cpc. If they don’t see a green and yellow wire, they mark it down as no cpc.
Thank little spark, I believe the budget won't run for. a rewire this year but they are well aware it needs to be done
 
The boxes may be metal, but is there an insulated block for the faceplate screws to go into? Thus electrically separating the screws from the box itself.

Another thing they used to do was use plastic screws….

And of course, only class II switches and light fittings. No fancy decorative metal plates.



I think nowadays, the consensus is to recommend a rewire when no cpc present…. And sometimes, it’s not actually difficult if the wiring is in conduit.

Speaking of which, a lot of “new” testers don’t cotton on to the fact that continuous steel conduit IS the cpc. If they don’t see a green and yellow wire, they mark it down as no cpc.
Reminds me.... are we still expected to test at 20A on conduit used as cpc? I can't instantly see it referred to in GN3 or s.6 anymore.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
EddieB,
Last reply from
7029 dave,
Replies
9
Views
270

Advert

Back
Top