Could someone help me clear something up please? On the NICEIC training - don't groan, I know it was rubbish - we were told to use to ac isolators one either side of the generation meter but when I look at kits they always have just one isolator in them. So should it be one or two?????
 
( 1 DC isolator per string DC side)

1 Main AC isolator at origin of Ac circuit

DTI guide says;
If the ac switch disconnector and the inverter(s) are not in the same room
a local isolator should be installed adjacent to the inverter(s)
This is to facillitate maintenance of the ac cable run and inverter(s)
 
If you have system where the inverter is near the mains board and meters, you only need one. If the inverter is in the roof you need 1 x AC Isolator in the loft space and one at the mains board, this is a safety measure so no one can turn the power on by mistake, they have to be lockable too.
Hope this helps!!!!
 
The system I've just done has two AC Isolators. One just after the inverter, in the loft, and the second one by the consumer unit downstairs. Obviously there is a DC Isolator just before the Inverter too.
 
Has anyone found a suitable alternative to replace the rotary AC isolator by the consumer unit? I have no problems installing one in the loft, garage etc, but quite a few customers I've encountered find them a little to industrial looking when their consumer unit is situated in their hallway, living room kitchen for example and I can't say I blame them!
Any suggestions?
 
I have fitted a couple of Santon units like this. Still not pretty but a bit better than most:
[ElectriciansForums.net] AC Isolators
Quite expensive and a bit cramped inside to work with, so I'll use something bigger and cheaper if possible!
 
Rotary switches are used as they can only be locked off, in the off position, ie can't use DP main switch for this reason .Also i can't think of another option ,there's probably several but why look when rotary's are stocked everywhere and they're cheap.
On our MCS inspection he said we could use 20A DP switch next to inverter but main ac isolator must be DP and lockable as above ie rotary
 
Thanks for the opinions people and thanks JCDC, I've looked at that isolator and as you mentioned it doesn't give you much room to work in! I think the problem is that this required degree of protection is not normally found within the domestic sector and we are therefore forced to use what is available currently on the market, namely big bright isolators designed to be easily identifiable in a factory! Not something that is adequate and will look nice on mrs Jones's wall! The search continues...
 
We have an installtion to do where the inverter will be in the loft space just above the utility box and the only sensible thing to do is to install henly blocks, a garage consumer unit, the total generation meter and an isolator in the utility box - see photo below.
[ElectriciansForums.net] AC Isolators[ElectriciansForums.net] AC Isolators
My Sparks has said that
it will be tight to get all this equipment in here, but we won’t know for sure until we try.

Just have a back up plan in case it doesn’t all fit in. may not require an isolator as the mcb in the garage unit would act as that, you would need to buy an mcb locking device and padlock
Has anyone used lockable MCB's yet? Why wouldn't it comply?
 
Before you go ahead with this idea you need to check with the DNO as I'm fairly sure you are'nt supposed to put any equipment other than switch fuses in there although I have seen consumer units in them worth checking though as they all have different policies
I have done this and got the ok to do so ,and managed to fit in an AC isolator /meter and 3 mod CU in similar space to the picture, he'll have to lower the meter to make it easier

As for lockable Mcb's they should'nt be used as they can be locked in the on position
 

Reply to AC Isolators in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
422
Hi all. OK... Let me just try and clear a 1" square space on the screen inbetween all the highly intrusive ads.... On a site (NHS in fact) and...
Replies
0
Views
395

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top