Hi guys, i have just installed my first pv system for a company that has just been set up (used for mcs accreditation all passed fine) The problem is the system is only generating 800watts an hour on a very nice sunny day. Its a 3.8 ish system with fronius ilgt3.6 inverter. The panels are 17 x 230 watt upsolar panels. The connectors on the panels werent compatible with the standard mc4 connectors so i chopped them off the panel yesterday and changed them so we now have better connections, the weather was awful yesterday so dont yet know if its made any difference. Anyone got any other ideas as to what it could be? shading is not an issue, the roof is south west facing with 35 degree incline, down in cornwall so it should be producing far more than this!
Thanks
Tom
 
hi, yes its on one string. Do you mean voltages? cant remember exactly now but it was around about 600volts from the panels, which i thought sounded about right.
 
waiting for my dc clamp meter so i can do the short circuit current, we didnt do irradiance tests but surely just down to the fact that its south west facing, 35 degree pitch and no shading it should be producing a hell of a lot more than it is?
 
Hmm, really difficult one. First thing I'd do is get an irradiance meter and a DC clamp meter and go and do some tests. This should give you a bit more of an idea what the problem might be. To be honest, you're going to need to do them anyway when you send the DC test forms off to the DNO.

Your voltage seems ok.

The problem may be with your connectors. The UpSolar 230w panels use MC4 connectors, is this what you used?
 
Hi, sorry internet has been down last couple of days. The panels came with rubber mc4 connectors that screwed together, but the mc4 connectors they supplied us to joint the cable were the plastic type that clip together with 2 'prongs'. I have changed the connectors on the panes on the end of the string for the same plastic ones now.
to do the short circuit current can i literally plug the string in end to end and put the clamp meter round it? does that not cause a problem with arcing when i disconnect?
thanks
tom
 
Our crews use a simple test box with a DC isolator and probe leads with MC4's on so we can do Voc and Isc quickly on every panel before it goes on the roof, as well as once strung : [ElectriciansForums.net] low generation

Sounds to me like your rubber MC4's that 'screw' together were MC3's ...
 
Last edited:
Hi guys, i have just installed my first pv system for a company that has just been set up (used for mcs accreditation all passed fine)

I'm intrigued by this company - do you work for them or just use them for the MCS accreditation?

Upsolar are supplied with MC4 - one is a prongy one like you describe, the rubbery ones are MC3 like Worcs said. You may have a dodgy connector or perhaps you've strung 8 panels and the rest are disconnected.
 
I initially thought they were mc3's but i got some mc3's from the wholesaler to make the leads up with those and they were far smaller than what we had on the panels. Think i might have to make myself up one of those!
 
Got a photo?
 
not at the moment, will take one when i go back there to have another crack. The company set up and i subcontract commissioning the electrical side of things.
 
I find it quite strange that you do not already have the test kit and are unsure about arcing, connector types and overall testing. How can the panels be installed an commissioned if the testing has not been done fully or correctly? This is probably the reason you are having problems now.

Best thing is to unplug the dc at the inverter an test Voc, then short, go outside and test Isc while noting panel temp and irradiance. From this you can compare your results against that of the manufacturers data sheet at STC according to the panels on the string.
 

Reply to low generation in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top