Many thanks for the reply Richard,
I didn't quite understand the last paragraph. I was planing on just running the cable in a daisy chain. Distance between each light is between 5m and 50m and the lights vary between 70w and 150w. Are you saying to run more than 1 cable instead of a daisy chain. Is it possible to use 2.5mm SWA as I have about 200m of it already or will this overload it?
Thanks.
From the voltage drop calculation I have done which is the worst case scenario you would need to use 10mm2 SWA to comply with the voltage drop requirements, as this is a very long run. Obviously the current carrying capacity of the cable would be way over the top and so the cable would not be fully loaded which would give you a slight advantage and may allow a 6mm cable (I have not done this calculation so this is an idea not a recommendation), however this is a very complex calculation to allow for the reduced load.
I attach a picture below to try to explain what I mean about the break down of the circuit, this does not mean running extra cables just calculating each section of the circuit individually and then summing.
The last section of cable with just one light on it will only carry the current for that one light so the volt drop will be much smaller on that section, as you move closer to the CU the current will increase, as you have more lights on the cable and so voltage drop will increase.
I do not know the spacing and wattage at each light but assuming a ten 100W light string only the run to the first light will carry the full current, dropping down thereafter at each light
B to K are the distances between each light, the values of the current carried are shown in the calculation.
The Vd for 2.5mm2 SWA is 18mV/A/m
It is unlikely that you would be able to comply with the volt drop for the whole run with 2.5mm SWA as the total basic volt drop would be 23.4V, however you may be able to start the first 100m with a thicker cable and reduce to the 2.5mm at the end.
Work out the distances between each light and the total current carried in each section (I=P/V), if you are using different csa cables then you would need to do the complete calculation for each section and not use the shortened form I show in the diagram.
i.e. Vdsection = Vd * A * m /1000 for each section and sum the results, this should give you a much lower volt drop.