So basically a 2.5 spur from the cooker point would be ok, especially if it was only powering an extractor.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Can i take a Fused Spur from a 45Amp Cooker Point in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
as long as it has upstream overcurrent protection IE a switch fuseSo basically a 2.5 spur from the cooker point would be ok, especially if it was only powering an extractor.
So basically a 2.5 spur from the cooker point would be ok, especially if it was only powering an extractor.
looks like youve answered your own question davenow i can understand some of you saying the cooker circuit is a dedicated circuit, but like i said in my last post, some cooker switches come with a 13Amp socket outlet on them. so thats not part of the dedicated circuit, because theres nothin to stop some pluggin whatever they like into that outlet. im using just a cooker switch with a fused spur thats going to be rated at something like 5Amps, dnt really see any difference.
and to Electro i always try and use the same size cable to the supply side of the fused spur as from where im spurring from.
Dave
If the circuit is protected by a 32A MCB, how come we are allowed to spur off of a RFC or the MCB with 2.5??
looks like its down to personal preference mark. i say no but others say yesthis was my point also
and a fused spur is being used so its better protected still
so the conclusion is yes or no?
i like that jason, "virtually no way"Considering what has been pointed out in the previous posts, i would say yes its fine, especially in this scenario as there is virtually no way anything else will be used on the spur other than the extractor.
found this last night, seems our mate trevor linsley thinks its ok to put a 12kw cooker on 2.5 or 4mm t/e
i know that jason, just posting what one of our senior instructors and lecturers thinksIf the correct voltage is used (230) this is nearer 52A.
However, it would still be mad to install a 2.5 cable to a cooker, especially if in the future a different appliance is fitted.