Not got my reqs or on site guide with me today could some one explain or show me an example to work out earth size 230v supply ze = 0.12 customer been told about calculation rather than need to upgrade earth system and i cant remember formula or how to do it thanks in advance lads
 
I = 230/0.12 = 1.92kA.

S= sq.rt. ( Isq. x 0.1 ) /143.
 
Last edited:
telectrix thanks for help but how would i calculate what size earth cable to use for installation by the above formula not done this before allways put in 16mm main earth 10mm water and gas thanks
 
Minimum earth size using the formula and values tel has given from you readings is 4.24mm2 anything above that and you can assume adequate but if fitting would need to be subject to minimum size for earthing system.
 
richard thanks for advise but coukld you explain step by step how you got that if you dont no ask always been my policy once ive been shown will store in my human hard drive many thanks
 
there is no set values for main earth, just main protective bonding, minimum 6mm for tns,tt and minimum for tnc-s 10mm,

the valuers are in the book if you cant be bothered too count
 
there is no set values for main earth, just main protective bonding, minimum 6mm for tns,tt and minimum for tnc-s 10mm,

the valuers are in the book if you cant be bothered too count

except it is a minimum of 4mm2 for any unprotected protective conductor according to 543.1.1.
 
With TN-C-S the minimum is 10mm², as the earth conductor is treated the same as a bonding conductor.
However, a smaller CSA could be deemed as adequate, if there is no evidence of overheating.
 

Reply to Adiabatic formula in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
248
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top