i want to fix an extractor fan in a bathroom. i cannot vent through the roof so can only vent through the outside wall and then only directly over the bath which is in zone 2.
the extractor will be about 1.5 metres above the bath
i intend to power off the lighting circuit which is already protected by an RCBO 6 amp.
is it ok to fit a 240v extractor (as i have the RCBO) or is a 12v required.
i would welcome your thoughts.
 
A court case.... The guy who fitted a fan on a 6A MCB and it burnt out causing a fire was prosecuted for not following manufacturers instructions. That is why 3 amp MCB's are now made.
I have some 3A MCBs that must be at least 15 years old so not a new innovation, just the resurfacing of an o1d idea.
 
i would probably lodge a counter claim to the manufacturer of the fan about why it burnt out!! its got to go faulty to catch fire... and if it goes faulty it will blow a 3a fuse and drop a 6a mcb if it shorts as the current overload will be massive..!
 
i would probably lodge a counter claim to the manufacturer of the fan about why it burnt out!! its got to go faulty to catch fire... and if it goes faulty it will blow a 3a fuse and drop a 6a mcb if it shorts as the current overload will be massive..!

Common sense would agree with you. However, the point was he contravened the regs by now following manufacturers instructions... A point I keep making when people say they can get away with 6mm on an 8.5 KW shower. Maybe you can, but many instructions now tell you to only use with 10mm cable.
 
[ElectriciansForums.net] Extractor Fan in bathroom
probably not as you would have to Fuse BOTH live conductors and it would make it bulky and it would have to be made larger to fit a 2g back box rather than single...!

You could fuse a comm then com feeds L1 so would only need 1 fuse, maybe have to make the switch a little smaller to accomodate the fuse
 
Last edited:
lighting feed into sw fused spur (3a fuse),load to bathroom light,twin to pull sw and 3core from bathroom light to fan.I know the bathroom would be in darkness if switched the spur off but, so what. Would satisfy most cases
 

Reply to Extractor Fan in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Thanks for your advice guys. very helpful
Replies
4
Views
1K
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top