Too many loaded questions/comments Glen, in my opinion....I would hazard a guess that you know what the guy is getting at though to be honest. The fact is that TL inverters have an inherent AC leakage current, ask each manufacturer what it is and they will normally tell you. Let's say, for argument's sake, that it is 20mA. On start up, especially on moist/misty mornings, where parasitic capacitive leakage currents can be naturally generated by the PV array, these currents when combined with the inherent leakage current generated by the TL inverter can exceed the 30mA trip limit and "nuisance" trip the RCD. SMA and others recommend a trip limit of at least 100mA because of this. PowerOne recommend 300mA.
Is the discussion about whether it is possible to increase the RCD trip limit without contravening any applicable requirements for "human protection" under BS7671? Or is it about whether TL inverters have inherent leakage current? No-one suggested that the auto-response was the increase the trip limit regardless. I think there was a mention of conforming to reg's and/or having a TT supply.....
I'm pleased to read that you use Type-B RCDs when fitting TL inverters, can I ask whether you would like to share why you do that please? Is that something you do for all TL systems or just ones where you deem it necessary to fit an RCD according to BS7671? Just curious, thanks.