Voltage drop | on ElectriciansForums

Discuss Voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

pencilpusher

Hi all

If an outdoor circuit comprises 2.5mm SWA running to adaptable box where it then splits into 2 x 1.5mm SWA cables for lighting, socket etc. how is the VD calculated?

I presume the VD for the 2.5mm run is calculated up to the adpatable box and added to the 1.5mm VD for each additional cable run present?

I would normally calculate on the smallest cable size present as a worst case scenario but was wondering what the alternative way is for the cables present.

Thanks

PP
 
Last edited by a moderator:
Supposing though that at the end of each leg of the smaller cable you had the same load, then wouldn't it be conductors in parallel? For arguments sake, if it was a 100W lamp, then wouldn't you be doing the calcs based on 200w down 3mm?? (also assumes both legs the same length).
 
Mostly voltage are drop at your homes because of the more than load of energy when you use the energy overloaded then you face the drops of voltage

Please may we have that again, only in English this time?
 
Mostly voltage are drop at your homes because of the more than load of energy when you use the energy overloaded then you face the drops of voltage

I know what voltage drop is and why it occurs. I don't, however, understand a word of this!
 
Last edited by a moderator:
Supposing though that at the end of each leg of the smaller cable you had the same load, then wouldn't it be conductors in parallel? For arguments sake, if it was a 100W lamp, then wouldn't you be doing the calcs based on 200w down 3mm?? (also assumes both legs the same length).

Hmmm, this has got me thinking now! Views?

PP
 
Last edited by a moderator:
It gives the same VD...

haven't done the maths so happy to be corrected, but if you go by the BGB tables then they are non-linear, so not sure about that.
 
Yes, in my tables the resistivity differs between 18.1-18.3 mΩmm²/m depending on the csa. But there is no meaning in trying to calculate the VD with a mV precision.
 
Yes, in my tables the resistivity differs between 18.1-18.3 mΩmm²/m depending on the csa. But there is no meaning in trying to calculate the VD with a mV precision.

Thanks but that is not the point though. My OP was about the correct way of doing it, not weather it was worth bothering with precision. I will stick with adding the VD up as previously mentioned.
 
Last edited by a moderator:
^^^ agree entirely. But it's been a slow day here at Rockingham Towers, so......
 
I thought voltage drop was what happens when the CU is upstairs, and all the sockets and lights are downstairs, so the volts all drop down the wires to the electrical stuff. Anyone know where my electric stopcock is?

Cheers.........Howard
 
Anyone know where my electric stopcock is?

should be in the attic. water flows downhill as well as volts.
 

Reply to Voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
520
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
460

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
234
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
880

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top