Discuss pme export in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

S

sedgy34

its advised to install an earth rod not compulsary unless there is a window in the roof where direct contact could occur, there is argument that bonding class2 equipment could cause a potential too.

if the array is not accesible i wont be installing any earth electrode in these circumstances as its class2 modules and out of reach.
any maintanance works to be carried out both AC/DC would be isolated on this instance!!!
 
we used to bond all TL systems to an earth rod or MET as per the 2006 DTI guide.

We stopped this when the draft new guide came out last autumn, and now follow this guidance as it actually makes sense, and we will now only bond where it's an extraneous conductive part (so tests positive for conductivity to earth), and is within touching distance of a velux window or similar.

I see exporting the equipotential zone to the roof as being something that should only be done where absolutely necessary, as it could pose a far greater hazard itself (in the event of an earth fault elsewhere in the house, and someone stood on a metal ladder touching the frame) than the odd minor tingle that it's possible to get in dewy conditions from capacitance from the panels.

so I think I agree.
 
its advised to install an earth rod not compulsary unless there is a window in the roof where direct contact could occur, there is argument that bonding class2 equipment could cause a potential too.

if the array is not accesible i wont be installing any earth electrode in these circumstances as its class2 modules and out of reach.
any maintanance works to be carried out both AC/DC would be isolated on this instance!!!

Do you still bond the array at all?

Where can i see the new dti guide position on bonding the array i cant find it :/
 
Had one today, with velux, so bonded back to MET, Will be nice not to have to worry about bonding otherwise.

Cant see how this can be completely safe though.
 
[ElectriciansForums.net] pme exportHeres the decision tree from draft guide
 

Reply to pme export in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top