What would everyone say the codes would be for the following:

1) tails 16mm not broken seals to check main fuse but if going on 100amp code c2 ?

2) old bar heaters in bathroom. code c1 ?

3) no supplementary bonding to pipe work at sinks in bathroom. code c3 ?

4) cracked socket code c2 ?

5) cooker circuit also feeding two sockets in up bedroom ?

any recommendations

Board has rcd protection to sockets, bar heaters but not to lighting or cooker circuit.

Thanks.
 
1. Cant code till you know for sure really , otherwise its just a guess.
2. Depends on if its in a zone , C2 if it is , C3 if its not.
3. If no rcd's for all bathroom circuits then code 2
4. Yes , C2
5. C2 if cables to sockets are in 2.5 or less , C3 for sockets having no rcd.
 
Last edited by a moderator:
1) Tails 16mm, I would LIM this as you cannot be expected to remove the fuse to check on an EICR, The DNO's think that 16mm on 100A fuses is just about OK anyway, (check the size of their service cable!)
2)I would C2 this if in a zone, c3 if not
3)C2, unless the readings between all Extraneous conductive parts and Cpc's of bathroom ccts. come out at less then 0.05 (usually means there bonded where you can't see)
4)C2
5)would depend on if the sockets are fused down or just direct spurs or spur on spur, if they are fused down no code (maybe observation), if they are a direct unfused spur no code (Observation) or if they are spur on spur in 2.5mm C2. If they are in 6mm or 4mm, No code.
 
Do any of these people bother to come back and read the answers we've kindly given ?
Or am i just talking to myself lol.
Totally agree Biff i think a [ElectriciansForums.net] eicr cding help is in order!
 

Reply to eicr cding help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top