Had a cracker of a job today | on ElectriciansForums

Discuss Had a cracker of a job today in the UK Electrical Forum area at ElectriciansForums.net

Amp David

-
Mentor
Arms
Joined
Oct 2, 2009
Messages
5,115
Reaction score
911
Location
Glossop
Quality one today.

Went to move shower isolator for my brother as hes doing a new bathroom. Ends up being a pig of a job as bathroom is in an extension, with a flat roof and the bathroom ceiling is timber clad.

Goes down stairs looks at CU and right away see this huge old iron service head. Then i see the nice new 16 mm earth along side the new tails, but then can't seem to see the earth connected to head or supply cable.

Ze tests at 13.9 ohms. Quality I think.

Out comes the circ saw and I take up the boards around the service to see if its and old 951 clamp hidden away, but no, nothing. So got the work light under the boards to be greeted by this beauty!

[ElectriciansForums.net] Had a cracker of a job today

951 clamp onto the lead water service in the floor void. This being used as the earth connection.

They spent 3k on a rewire earlier this year. Not a single cable entering the CU is new, not only because they're all the old colours, but they're all still painted up in emulsion paint. Then I find no bonding to either gas or water and only half the new CU has RCD protection.

Had DNO out who confirmed that there had never been an earth supplied since day one, yet no earth rod insight. Good thing though DNO are back out tomorrow to sort an earth and change service head.

Since getting home tonight, my brother has gone back to update the customer regards his so called rewire and got to speak to the spark who did it. He blamed the testing on another guy who tested it all, confirmed that because there was no supplied earth they had used the water supply and when asked what readings he got for their Ze, he started stuttering and all of a sudden was lost for words.

This pics also makes be wonder. Its a dual RCD chint CU, but in place of the first RCD their seems to be a 63 amp C typre DP MCB instead. God only knows what his plan here was.

[ElectriciansForums.net] Had a cracker of a job today
 
That is shocking. Obviously there is some paperwork to back-up the "rewire"?
Looks like a full refund is in order here...
What's really sad, is that these cowboys are taking work away from good electricians who are trying to decide whether it is worth carrying on in business....
 
So, to summarise...

1) Customer paid for a rewire which didn't happen...
2) "electrician" (I use the term loosely) connected main earthing to lead water pipe....
3) It was left as a "sort of TT system", but only half the board is RCD protected....
4) "electrician" (I use the term loosely again) didn't understand what Ze means.

To conclude....

The customer was robbed and put in danger.
Now, you can't tell me that there isn't somebody who will take this state of affairs seriously???
 
That is shocking. Obviously there is some paperwork to back-up the "rewire"?
Looks like a full refund is in order here...
What's really sad, is that these cowboys are taking work away from good electricians who are trying to decide whether it is worth carrying on in business....



Oh the certs, yeah whats one of them.

When mentioned to him that the DNO wanted to see the test certs for the rewire before they would reconnect to the supply, he started to sound a little nervous.

He actually reckons that he will make an appearance back at the house tomorrow.
 
Oh the certs, yeah whats one of them.

When mentioned to him that the DNO wanted to see the test certs for the rewire before they would reconnect to the supply, he started to sound a little nervous.

He actually reckons that he will make an appearance back at the house tomorrow.

I hope the customer is there to ask (if the cowboy does show up) how the new cables look just the same as the original. I'm sure there is a term for taking money for work you haven't actually done....
 
I would like to say I'm gobsmacked, but I'm not. Nothing surprises me now but it still gets my blood pressure up... :(

How many threads/posts have we had on dodgy installs in the last couple of weeks?
 
They spent 3k on a rewire earlier this year. Not a single cable entering the CU is new, not only because they're all the old colours, but they're all still painted up in emulsion paint. Then I find no bonding to either gas or water and only half the new CU has RCD protection.

Not sure if I'm missing something here, but those cables look brown and blue to me...
 
One question arises. If they have had a rewire were there not signs that one had been carried out such as a few more sockets dotted around, new sockets switches and light fittings, sockets in different places from where they were originally, chases waiting to be plastered/new plaster on chases etc etc?
Every rewire I have ever carried out has resulted in all of the aforementioned. I appreciate that the "victims" were not clued up electrically but surely there must have been signs.
Actually that's a few questions really isn't it?
 

Reply to Had a cracker of a job today in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
982

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top