Hi chaps

Having quite a heated discussion with a colleague about a 4 pole RCD. He originally installed a 30mA RCD which now needs to be changed to a 100mA, however the N is on the opposite side. He seems to think that putting L1 into N of the RCD, L2 into L1, L3 into L2 and Neutral into L3 would be ok, and the RCD would still work.

What are your thoughts?!

Cheers
Mark
 
Hi chaps

Having quite a heated discussion with a colleague about a 4 pole RCD. He originally installed a 30mA RCD which now needs to be changed to a 100mA, however the N is on the opposite side. He seems to think that putting L1 into N of the RCD, L2 into L1, L3 into L2 and Neutral into L3 would be ok, and the RCD would still work.

What are your thoughts?!

Cheers
Mark

The test resistor is normally across 1 phase and neutral so if you satisfied that it would work/if you didn't and picked up 2 phases ! BANG lol...........why someone would contemplate putting a ~Live into a Neutral connection is another matter !!!!!!
 
This is a Wylex 4 pole, as long as the neutral was at one or other end it would work, but each make may be different;

[ElectriciansForums.net] 4 pole RCD
 
What a numpty i hope said bloke isnt an electrician as hes an embarrasment to the trade, and please dont tell me he qualified too :90:, you entertain the idea of fitting live terminals to connections marked N, it may work on brands with 4pole disconnection but will simply contravene the regs as you havent followed manufacturers instructions. At worse you could create a potentially very dangerous situation.
 
[ElectriciansForums.net] 4 pole RCDHere's one that would go bang if you pressed the test button if you wired as your mate suggested, to note the test button is wired across 1ph and N so changing this set-up as suggested would put 400v through the test resistor and blowing it.
 
Interesting the different set ups for the test buttons on the wylex ( across 2 phases ) and the one you've highlighted.
My 4 pole rcd's have the test button between L3 on the input side and Neutral on the output.
That's to facilitate using it as a 2 pole device if you want to........wiring to L3 and Neutral only which would still allow the test button to work without the need for an external resistor
 
It highlights the various designs and hopefully the OP will take this in for his defense in his heated debate but anyone not wiring as designed by manufacturers is a bit of a bodgit and scarper regardless of whether it might function on some models, had they pre-empted the N position then they could have ordered the correct one in the first place rather than trying to cover their mistakes by cutting corners.
 
Print off the example images we put up on this thread as they back our comments up, he isnt incorrect that it can be done but it would contravene regs and is only applicable to certain models of 4p-rcd's but to preach this to you without further explaining the points we have shown you here is shortsighted and poor judgement, so i can only assume he actually believed what he was telling you to be correct across the board.
 
There is also the possibility that the neutral line has a different switching mechanism to the phase lines, which is not shown on the diagrams... Crazy to connect a phase line to a terminal clearly marked with an N!! lol!!
 
I've seen many 2pole RCD's wired opposite which isn't so bad because its just a switch.....granted still bad practice and potentially dangerous and anything installed should comply with the manufacture's instructions and/or the regs. But to wire a 4pole RCD wrong is just plain stupidity. Charge a capacitor and throw it at his face.
 
If it were 4 pole then it would be OK, if it’s 3 pole and neutral it wouldn’t. 3p+N the neutral is late break, early make.
As for the voltage of the test circuit, they allow plenty of leeway in the resistor tolerance so highly unlikely to cause damage. If the RCD is working correctly the test disconnects with it opening. I.E. mili seconds, no time for it to burn out.
 
I Quote from Schneider Tech' data sheet with regards to their 4pole rcd unit -
Nominal voltage - 415v
Test button operation voltage - 115v to 264v
(They also do a mgv 4p range with test button voltage of 112 - 456 just to clarify it only effects certain rangers)
Sending 400v across the test button only rated to 264v could damage it to a point it fails or could give a false positive reply when the rcd is actually faulty (it trips even though the rcd may not be functioning correctly) so if you haven't got a meter to check this then you may assume its ok -i.e. the customer doing a quarterly check.

So in this particular case il stand by my responses that you shouldn't swap N with a L even if you discarded the regulation re' following manufacturers instruction which does over-rule the argument anyway.
 
Last edited by a moderator:

Reply to 4 pole RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top